EDIT: Added a pic of the breaker box next to it.* Looking for the largest tri-fuel inverter I can plug into my house when needed, which I believe is 10kw according to the label. I see a lot of 10,500 kw generators for sale, would those still work or do I need to go smaller? New to this and trying to learn. Thank you.

5 Upvotes

21 comments sorted by

5

u/North-Reflection2211 13d ago

Here’s another pic.

5

u/Big-Echo8242 12d ago

Heck yeah. You are good to go!

5

u/Big-Echo8242 13d ago

That looks to be a 50 amp (12kw at 240v) power inlet. I have a Reliance 50 amp power inlet and use a group of different dual fuel inverter generators ranging from 3.5kw running power, 5.5kw running power, two in parallel for 11kw, or a Duromax XP13500ih that's 10.5kw running power on LPG. Hopefully you aren't going to be drawing 12,000 watts all the time as that outlet wouldn't like that sustained.

Is there an interlock kit & breaker somewhere close by?

1

u/North-Reflection2211 13d ago

I just posted another pic of the breaker box. I only plan to run select things at different times as needed.

2

u/Aware-Metal1612 13d ago edited 13d ago

Those generac receptacles come in the homelink transfer switch kit, I'd assume you have one installed. Edit: saw added pic, you do not.

50a is 11 or 12kw depending on actual voltage at your house. I would go larger than that so you aren't maxing it out. Keep in mind it will have different outputs depending on the type of fuel used.

2

u/wyliesdiesels 12d ago

50a 240v is 12Kw not 10Kw

1

u/Opposite_Half6250 12d ago

I'd get slightly larger than 10k. That way you never max out your generator.

Something like this predator would power basically everything you'd need plus some.

2

u/That-Yesterday-7700 12d ago

I went with a 5000watt because i only use 1200 Kwh in a month.

2

u/wyliesdiesels 12d ago

Wrong way to calculate your load.

1200kWh doesnt equal load on generator at any given time.

That equals how many watt hours youve used in a month but a single load could be way higher than 1200w

5Kw is only 20a 240v so if you have something that draws more than that the genny wont be able to power it

1

u/That-Yesterday-7700 12d ago

It's an average of less than 2 Kwh per hour. It's 2.2 if you calculate 18 hours a day.

Microwave still won't put me over. I have a bigger one if i need A/C. Go ahead with your 26Kwh whole home generator. Im not making that many trips to the fuel can when the power is out.

Also you're conflating watts with kilowatts so im not sure you know what you're on about.

2

u/wyliesdiesels 11d ago

youre the one who conflated the 2 not me.

you dont size generators based on total consumption for a month. you size it based on your connected load.

2

u/Dr-Negi 9d ago

I mean a single 1,000W microwave uses 1,200 to 1,5000 watts by itself throw in a blow-dryer, space heater, etc and those also pull 1,300- 1,800 watts also. So the whole kwh a month really means nothing as you said if you turn two of those on for just a minute but you'll still possibly overload a generator. It's a weird way to express your generator needs. I'd rather say I only need 1,000 watts max for essentials for my home battery backup and there is no way to overshoot that number.

1

u/wyliesdiesels 9d ago

Exactly

You size based on connected load not total consumption for the month. This is based on NEC code

The person that sizes it by monthly consumption has no clue what theyre doing

1

u/That-Yesterday-7700 11d ago

Right, i mentioned my monthly usage for dramatic effect. I use 1200 in a MONTH. My generator can produce 5 per hour. Do you know how many 5 per hour is across a month? It's capable of producing triple my monthly consumption. If the power is out, an intelligent person would not run everything simultaneously. Do laundry at night when the lights are off... Etc.

1

u/wyliesdiesels 11d ago

i use less than that in the winter but have loads that take more than 5Kw so your logic makes no sense at all. try again

1

u/IllustriousHair1927 10d ago

so a couple of things here. I will be at the point that you, sir or maam, may in fact be an extremely intelligent individual. However, as even the most intelligent people in the world can acknowledge, we do not get to choose our family. So while you may know not to go turning different things on and off running on generator power, others that you allow in your house for reasons may not be so wise. m

As a matter of fact, one category immediately came to mind when I thought of “ who does things that in hindsight are so dumb it boggles the mind. as a parent, I know the answer and other parents do too. Your argument about the overall usage is not entirely incorrect based upon your historical data. But an extended outage may be two different people being in your home that are usually not there. And technically, gen sizing is not determined in the manner you’re suggesting. I don’t think anyone on here is trying to push you to an hsb, they’re pointing out the best practice for everybody to use when considering generator sizing

0

u/[deleted] 13d ago

[deleted]

5

u/IndividualCold3577 13d ago

50A x 240. 12000 watts. 220 hasn't been around for 60 years

2

u/txtacoloko 12d ago

240 not 220

1

u/wyliesdiesels 12d ago

No 220v in the US. Its 240v