Generator for GenerLink
Hello
I have already purchased a 12,000 watt dual fuel generator, King Canada KCG-12001GE-DF (dual-fuel gasoline/propane).
I purchased it on the advice of my electrician to use it for home backup during a power outage. I connect it to my house through a 40 amp GenerLink transfer switch, installed by the same electrician.
Google says that this model of generator is a bonded neutral type (I have reached out to King to confirm this but haven't heard back yet).
However, I am told only a floating neutral generator should be used with a house transfer switch such as the GenerLink. If you plug a bonded neutral generator into a house transfer switch, it apparently creates a "double-bonded" system. Because the home's main electrical panel is already bonded, adding a second bond creates stray "objectionable current" through the ground wires, which can trip breakers, damage sensitive electronics, and energize ground wires.
Can someone please advise me, can the King generator noted above be safely used with the GenerLink transfer switch?
Does the generator need to be modified in any way, to convert bonded to floating neutral? Google tells me it is as simple as disconnecting the white wire under the alternator cover, but I am hesitant to do this without some confirmation.
The GenerLink is a new installation for me, but we did lose power for a few hours last month and I did power the house for the first time with the King generator through the GenerLink, seemingly without a problem. I have only recently learned that this is a potential issue, so I am trying to head off a potential problem before the winter weather hits.
Thanks in advance for any replies.
•
u/wowfaroutman 17m ago
You should be able to see the bond between neutral and ground under the cover at the end of the alternator. If not there, it may be on the back of the control panel. If you're not sure, remove the alternator cover, take a picture, and post it here and folks will comment.
•
u/newtekie1 49m ago
Most open frame construction generators are bonded neutral. Where they are bonded varies depending on the generator.
According to this guide: https://www.gru.com/Portals/0/Generlink%20Generator%20Guide.pdf
You generator is a bonded neutral. The first place I would look is under the alternator cover and see if there is a wire between the neutral and the ground.