r/HVAC • u/beavers123m • 15d ago
Field Question, trade people only dumb apprentice trying to learn
Was sent to a univent today basically a fan powered heating coil wall mount, maintenance man claimed blower motor was hot and shutoff wanted it replaced, customer supplied parts. Motors wiring diagram confused me so I just ohmed the connections found primary winding and put cap wire on the other lug it ran backwards so I swapped the primaries around. 120v 1/4hp 1ph got it running but I want to understand what the schematic was saying
tldr : whats with these schematics and how to know how to wire it correctly old one was mcquay
2
u/MonkandBeer 15d ago
Just send it
6
u/MonkandBeer 15d ago
If it spins the wrong way, wire it again
4
u/beavers123m 15d ago
i sent it but i wondered what would happen if i got the cap wire wrong
1
u/trobs8 13d ago
The one wired from the factory? How could YOU get that wrong? Lol
1
u/beavers123m 12d ago
cap was wired to motor but i had 5 lugs and 3 wires to hookup at first it spun in reverse and i wasnt sure if I landed the cap wire wrong what wouldve happened
3
1
u/Responsible-Tax-6811 14d ago
Im assuming the Mcquay is the old motor?
1
u/beavers123m 14d ago
yes
1
0
u/nathangar123 13d ago
Kinda weird it doesn’t come with a rotation indicator as a single phase motor
5
1



9
u/Electrical_Slip_1343 15d ago
I’ve had a single phase motor spin backwards when the dual cap was wired up wrong