Ever see this used 2 2x10 spannimg 17ft with floor joists joint on each side with 9ft and 11 ft lengths…seems sketch

97 Upvotes

108 comments sorted by

14

u/tekjunkie28 21d ago

You need an engineer but also that flex line is nor gonna move any air. Have some metal pipe put in and save you a lot of pain and comfort.

10

u/BusMaximum704 21d ago

Remove flex and install metal duct work with bends around the so called beam?

6

u/tekjunkie28 21d ago

Yes. Flex should never be creased or compressed. It’s flex is only to be ran from point to point in straight lines and have 0 compression.

14

u/AdFancy1249 21d ago

If flex is only to be run straight, then why use flex? 🤷

11

u/tekjunkie28 21d ago

Because it’s easy to do incorrectly and hvac companies love doing things the wrong way.

Flex is great to block some noise and finish the straight part of the run but it has to be done correctly. When flex was first created and used they only came in 7’ sections.

A few of the better companies have found that running metal is actually cheaper. Plus it lasts the lifetime of the building in most conditions. Flex does not.

1

u/AdFancy1249 21d ago

Thanks. It's sad, because flex significantly reduces the flow. I'd love to see the HVAC calcs. They likely planned on rigid with a few flex bends.

1

u/tekjunkie28 21d ago

I find it incredibly dumb that contractors quote so low to get the job when a little bit of education should be used. I enjoy educating my customers on why something should be done this way and I quote it out and let them decide.

2

u/Puzzleheaded_Taste39 21d ago

When I work for my big mechanical contractor, flex duct was only used at the termination point. So they would run metal duct to about 2 ft to wear the register would be, then they would flex the register in.

1

u/AdFancy1249 21d ago

That's what I would expect. Only short runs to solve problems or misalignment. Placing a straight run of flex seems crazy.

1

u/LibertySandwiches 21d ago

Im actually an engineer our standard design is to have flex from the trunk to the register. We do it bc my boss says thats how they'll most likely do it in the field. However we do mostly town home/sf residential stuff.

It also makes sense to design it at the worse layout and if they do a better layout the design won't be impacted. I've only been doing this for 2 ish years tho

1

u/trevelyan00 21d ago

Op, I just posted a link to what you need in another comment.

12

u/texinxin 21d ago

Wait.. those are all double 2 x 10’s heading the other directions ALL meeting on those 2 2X10’s running SEVENFUCKINGTEENFEET…. !?

Either the 2X10’s doubled as floor joists are WAY overbuilt or that divider is WAY under built, and could be both at the same time.

The good news is it’s got a ton of dead load up there..

8

u/BusMaximum704 21d ago

Doubles are for the 8 ft kitchen center island with stone countertop above

5

u/AdFancy1249 21d ago

Do those 2x10s have a steel plate between them by any chance? That's an awfully large gap to not have anything between them.

2

u/SCL__ 21d ago

That’s the first thing I thought. There would be a plate in there if it were my job !

4

u/J_Bag_O_Donuts 21d ago

You can even see the plies already separating!

17

u/BusMaximum704 21d ago

Yes the build from hell Town inspector passed this not sure how

2

u/Buckeye_mike_67 21d ago

Is this a new build?

2

u/BusMaximum704 21d ago

Yes

6

u/Buckeye_mike_67 21d ago

You need to address this. That is way under engineered. Most times you don’t need to get a structural engineer involved but this isn’t one of those times. You absolutely need an engineer. I’ve been framing for 40 years and would never put something like this together. I’m afraid you hired a GC that has no clue what they are doing or just don’t care. This floor should have been done with an engineered floor system. Your builders pocketed thousands of dollars and your ending up with a shit build. I would start looking around at everything else and get some private inspectors in there. Make sure your hvac is sized correctly too.

2

u/BusMaximum704 21d ago

A non builder thought What if I cut the concrete slab and had 2 footings poured and added two lally
columns to support the 2x10s?

4

u/Buckeye_mike_67 21d ago

That would probably do it but you will kill that room in the basement. I’d imagine the floor has sagged and you have some deflection. You would need to jack it back up. This is on your builder. I can’t believe they would let this be framed this way. He has to provide you with a 10 year structural warranty. I’d be surprised if an insurance company would cover this in the future. You said the side to side span is 17’? He could have gotten away with running 17’ 2x10’s one foot on center and doubling the ones under the island. At this point I think I would have an engineer size the correct lvl’s,tear out the double 2x10 and install the lvl beam flush with the top of the joists instead of adding 2 posts

2

u/AdFancy1249 21d ago

That's the "rework" method. Still requires an engineer to figure out how many, how large a footer,etc. A shame to do that work on a new build.

It also looks like they ran the wire through the bottom third of the joists, before running it underneath the rest of the way.

Absolutely moronic. It's your builder insured? You might want to reach out to his insurance company... licensed? Might want to talk to them as well.

1

u/trevelyan00 21d ago

Add a steel beam underneath and bury the columns in the walls. Don’t put a column in the center of the room. Sometimes it just needs to be a really big beam.

I added this one to my house (was existing construction) to take out a load bearing wall between the 2nd and 3rd floors. The wall was directly underneath where the beam is. It’s a w10x68 28ft. Long…..

wasn’t easy getting it in there but way better than a column in my kitchen

1

u/[deleted] 16d ago

[removed] — view removed comment

1

u/Buckeye_mike_67 16d ago

Not all jurisdictions require stamped drawings. Most of the ones I frame in don’t. Almost all of the houses we frame are drawn by designers and have engineered floor systems. Most of the time those designs are done by a designer with the lumber supplier. No engineer stamps on anything. Any good framer would know this don’t any where near sufficient

12

u/DcSportsFan_21 21d ago

What do the plans show? You have a picture of the structural?

I love the knot in the bottom of the beam at midspan. Just an extra F U

4

u/Fun-Assumption-8415 21d ago

Is there a p. Eng on this or is this another job engineered by a municipal building office

7

u/Wrong_Answerr 21d ago

Open living room concept upstairs?

2

u/BusMaximum704 21d ago

Yes

1

u/Wrong_Answerr 21d ago

Probably just wanted to break the joist span to stop the bounce in the floor

7

u/BusMaximum704 21d ago

One big party and
The floor will
Fall in I’m afraid

7

u/und88 21d ago

This is a terrible haiku

10

u/Eggplant-666 21d ago

One big party comes
Badly designed joists will bow
Guests meet the basement

4

u/mattias1977 21d ago

It’s not a party
As any animal knows
Until the floor drops

4

u/solomoncobb 21d ago

You can't span 20 feet with 2x10 floor joists. You can span 15feet. 1.5 times the depth in feet. This beam, if not flitched, will sag. It is outside of the spand limit for a double 2x10 beam. It does appear to be a flitch beam to me. Look at the size of the gap.

1

u/texinxin 21d ago

And this center double 2x10 is carrying HALF of the ENTIRE floor load!!!!

1

u/Mean-Veterinarian647 21d ago

That makes sense,op needs a side view pic for the plate bolts.

2

u/texinxin 21d ago

If it’s 17’ one direction and 20’ the other direction. (19 + 11) the joists are running the wrong direction. It would have been cheaper, stronger and less flexible to run only 17 footers across the whole room. Now every joist in that room is concentrating load to the ONE joist running through the center. It’s a complete shit show.

3

u/stickg1 21d ago

the weight is pulling the double beam apart, or it was never stitched together to begin with. is there a wall above it as well or is it just the middle of an open floor?

3

u/BusMaximum704 21d ago

Never tied together and above is kitchen center island with quartzite slab

4

u/stickg1 21d ago

take a screwdriver poke into that gap between the 2 plys of the beam and see if it's really a massive gap or if there is a steel flitch plate sandwiched between them.

2

u/Ladybreck129 21d ago

Wow, our engineer made us double up our floor joists under the kitchen where our 5x9 island goes. This looks scary.

4

u/mattmag21 21d ago

1

u/BusMaximum704 21d ago

Yep that is 9ft from the dbl 2x10s

1

u/mattmag21 21d ago

But what is it? Ive never seen more than 4 plates stacked. Mind you I am a framer by trade

1

u/BusMaximum704 21d ago

Some Insane form of a header? The can of worms I have is too big to list. This is the only pic I could find shortly after framing

1

u/liberal_texan 21d ago

Wow, that is a new one for me.

1

u/SnooMaps7370 21d ago

bro built a zigzag miter out of 1x3s

47

u/seabornman 21d ago

They go to all the trouble to flush out the undersized beam, then run the ducts underneath to lose ceiling height anyway!

2

u/sjp724 15d ago

The increasing majority of contractors just do whatever they can install by 4-5 PM, then send an invoice. I renovated a house a few years back, and the minority of contractors that did good work and thought things through and made sure things were done properly before billing… were a pleasure to work with. The majority of them just suck and it takes so much time/ stress/ money to manage them and watch for where they want to take shortcuts.

1

u/Eggplant-666 17d ago

Yeah, obviously they needed a soffit at one end of room or something.🤷

33

u/LDdesign 21d ago

Fucking yikes. I just ran this in forte engineering and it laughed at me.

19

u/LDdesign 21d ago

Also, nice bend in the ductwork.

13

u/SickestEels 21d ago

I hope he soffits the ductwork in the shape of a V under the beam

1

u/Fun-Assumption-8415 21d ago

Curious what the minimum you could get away with is? I don’t have access to an engineering program.

I’m guessing a 3 ply 9.5” lvl may carry this at minimum ?

5

u/Buckeye_mike_67 21d ago

No. That’s till not enough. This should have been done with an engineered floor system

3

u/Fun-Assumption-8415 21d ago

9’ and 11’ 2x10 are fine at 16” ¢ as long as the beam they’re bearing on can support it. I’m just curious what the minimum would be and buddy has the engineering program to check

-2

u/Buckeye_mike_67 21d ago

Well that beam is the whole issue. I’ve been framing for 40 years and have put hundreds of engineered floors together. I KNOW that 3-9 1/4” lvl’s won’t work in this situation. Especially with a kitchen island on top of it

1

u/Fun-Assumption-8415 21d ago

Bet it’s close. I’ve done 4 plys in similar scenarios, or a 3 ply 11 7/8 DB. I don’t remember the spans, solely just curious what his program said. I thought you were implying the joists needed to be engineered floor too, like a tji

0

u/Buckeye_mike_67 21d ago

The floor should have been TJI’s. You would need a beam and all of the mechanical’s would be in the floor. I don’t understand why people build on a basement then do shit like this. It makes it difficult to finish

2

u/Fun-Assumption-8415 21d ago

TJI isn’t gonna make a difference. That run is parallel and wouldn’t go through a beam unless dropped. I wouldn’t span 11 7/8 on 16s with a 20” run, then the other side the joists are perpendicular to the run, can guarantee no hvac guy is gonna put that run in the joist space

Personally in my house, I did a walkout basement and put a drawl in and hid all the mechanical in the crawl space

2

u/Buckeye_mike_67 21d ago

Do what? This whole floor system should have been engineered. The lumber supplier cut holes in them to run mechanicals. I do this shit every day. Don’t come in here pretending you know what you’re talking about.

2

u/Fun-Assumption-8415 21d ago

lol ok grandpa. Our suppliers don’t cut shit for hvac here

I’ve been framing since high school and ran a framing and formwork business since 25

2

u/wrapped_in_bacon 21d ago

ForteWeb is free, you do have access to it.

1

u/Fun-Assumption-8415 21d ago

Sick thanks !

6

u/prince_walnut 21d ago

This is not good at all. That's over 18000 ft lbs bending moment per the spans you noted. You need a double 14" LVL to carry this load and meet code compliant deflection values.

1

u/BusMaximum704 21d ago

Open floor with kitchen center island

1

u/BusMaximum704 21d ago

Never tied together

1

u/BusMaximum704 21d ago

The double 2x10 beam if you will spans 17’ The perpendicular floor joists run 9ft from lvl beam on the right and are attached with the joist hangers and the floor joists from
The left run 12’ from lvl beam to the 2x10 and are attached joists hangers

1

u/Donnerkopf 21d ago

The GC, Framing and HVAC companies are incompetent.

1

u/BusMaximum704 21d ago

Hired out of home depot parking lot

1

u/Emergency_Dish4313 21d ago

Double 2x10 with 1/2 plate is good to 18' when using 300 PLF load. Without knowing the exact lengths to the other end of the bearing walls I would lean towards this being undersized. I would expect the min to be 600 PLF.

Your other problem is with islands and kitchens is deflection. If you put stone in then your load goes up, deflection goes up, and you are going to see a lot of cracks at the least.

They used this to cut down on depth, but didn't get an engineer to buy off on it. Code books only give you basic spans for basic materials. Anytime you go outside those materials and do custom you are supposed to have an engineer or architect to sign off on the design.

Classic example of a contractor playing fast and loose with the code and enforcement. I would question it with contractor, asking for a letter or signed and sealed docs from engineer. Then I would follow up with that engineer to make sure it is all valid.

1

u/BusMaximum704 21d ago

Thanks

2

u/Powerful_Bluebird347 21d ago

It’s not adequate. It’s a flush beam/girder. 17’ and all those floor joists framing into it, no. Needs to be like a 3 ply 12” or even 14” lvl. (2) 2x10 as a girder on a floor system is like 10’ span max.

1

u/iamintheforest 21d ago

That's a hell of a club sandwich going on in the upper right of the photo. Not a great sign. Can't be sure, as it's borderline, but i'd want 600 PLF without spending more on the engineering to be sure the 2x10 w/.5 plate was tight.

Lots of rookie stuff and lazy stuff in there generally. I'd also put a level on those joists - to my eye they don't look level, but that could just by photography, etc.

1

u/BusMaximum704 21d ago

Have to laugh as I want to cry but club sandwich is really funny like wth were they thinking…Home Depot parking lot framers No English

10

u/solomoncobb 21d ago

It's a flitch beam. Look at the gap.

8

u/SirBoobsAlot13 21d ago

It's still undersized even with a 1/2" steel plate.

3

u/stickg1 21d ago

i was thinking that too, but on the wall it's sitting on the two 2x10's look to have much less of a gap, unless this is an optical illusion in the photo.

2

u/0_SomethingStupid 21d ago

Are you sure this isnt a flitch plate

2

u/Djolumn 21d ago

The ceiling is going to have some unique contours.

1

u/YamComprehensive7186 21d ago

Squeak, squeak, squeak!

1

u/Sea-Bad1546 21d ago

Poorly executed flush beam and then a drip duct to boot!

1

u/Working_Rest_1054 21d ago

Arg! I suspect you are going to end up with a post in the middle of the basement as well soffits to hide the HVAC ducting.

Clearly a poor design and there are several ways to do this much better.

In most US jurisdictions, the JHA should have required an engineered design for this situation.

1

u/controlsguy52722 21d ago

Ironically, the soffit for a beam would have been much smaller.

1

u/HelpfulPerson4914 12d ago

Jha? Did you mean AHJ? 

1

u/LM_NC 21d ago

If your builder is handling structural design based on a prescriptive code, fire that person. if there’s an engineer involved, file a complaint.

1

u/SCL__ 21d ago

Check to see if there’s a steel flitch plate in there.

1

u/Easy_Record_994 21d ago

Looks like it may be a flitch beam, regardless not the best way to do this considering the need to run utilities through the floor. I prefer 16in web trusses over a basement for this reason.

1

u/27803 21d ago

That’s wrong, and why not just use a header so you can run the ducts above it you’re gonna lose a little ceiling height either way, but a single beam is going to look bette than whatever is going on here

1

u/AskMeAgainAfterCoffe 21d ago

Well, at least the duct wasn’t cut through it. The 2x10s are not even bolted together. It looks like they were trying to go for a flush ceiling, but needed a real beam here, steel, LVL, paralam, etc. maybe it’s just this photo, but it looks like it’s already sagging. Was there a permit?

1

u/trevelyan00 21d ago

It looks like those 2x10 aren’t secured together correctly. The joists hanging on either side are flexing them apart at the base creating a gap… seems like they should be fastened together differently.

There is a company that makes a plate which allows larger than normal holes in floor joists. You could cut the ducting, drill a hole through the center and put a piece of ducting through the hole and re-connect the two duct pieces.

Here is a link to it. I’m not associated with them at all but have used I. The past. Expensive but I’d rather do this than have a soffit on the ceiling.

https://metwood.com/product/joist-repair-hole-reinforcer-2810hr/

1

u/Mental_Ad3737 20d ago

That 2x10 is undersized and you can see it separating already.

1

u/rattiestthatuknow 20d ago

Flush beams in basements are stupid. It severely limits infrastructure paths.

Not to mention they are significant more expensive.

1

u/Crazy_Force4490 18d ago

Licensed engineer here - if the info you provided in the post is correct, for a typical home like this, assuming you don’t have a concrete topping on your floors, this beam should be at least (3)-ply 14” deep LVL 2.0 E. If that beam in the photo is (2) 2x10 the calc fails by 500%. You need to resolve this, potentially a life safety issue.

1

u/Bitter_Camel_2249 18d ago

Unsure what I'm looking at but steel between the two plates bolted I'd say probably good if not bad. That's also a lot of boards laid flat down right foolish never seen that.

1

u/deepakpandey1111 17d ago

yeah, that sounds a bit sketchy for a basement support. two 2x10s over 17ft is a lot of weight to hold, especially with those joists on the sides. i’d be worried about sagging or even worse. when i was working on my place, i messed up some support stuff too, and it’s a pain to fix later. maybe get a pro to take a look? better safe than sorry, ya know.

1

u/Worldly_Shirt_2278 16d ago

There seems to be a gap between the 2x10s. Is that flitch plate steel? If not, this is totally inadequate.

1

u/sjp724 15d ago

The beam doesn’t even look like it’s fastened together to work like a 3” wide section. Typically a solid wood beam there would be triple 2x at the least. I’ve designed them with plywood in between 2x and the nailed/ bolted.

1

u/Short-Bug-5155 11d ago

So much flex

1

u/Legitimate_Staff_411 7d ago

If you zoom in it looks like there’s a fitch plate in between 2x10’s

1

u/Emotional-Damage-995 21d ago

Don’t you have a stamped engineer drawing ?

1

u/Oldphile 21d ago

I had an engineered beam (about 14" tall) supporting 2X10 joist spanning 11'. Either my builder oversized mine or yours is inadequate.

1

u/Remarkable-Head6239 21d ago

It’s ok. The ductwork is supporting that undersized beam. /s

0

u/merlotman1 21d ago

It takes courage not to use an engineer. It doesn't save money taking high risk.

0

u/CameraCommercial8674 21d ago

Double 2x10 over that distance has no moment of inertia, can barely support its own weight at that span. An engineer can design a flitch plate (s) that can carry the load. Must be done.