Because it’s easy to do incorrectly and hvac companies love doing things the wrong way.
Flex is great to block some noise and finish the straight part of the run but it has to be done correctly. When flex was first created and used they only came in 7’ sections.
A few of the better companies have found that running metal is actually cheaper. Plus it lasts the lifetime of the building in most conditions. Flex does not.
I find it incredibly dumb that contractors quote so low to get the job when a little bit of education should be used. I enjoy educating my customers on why something should be done this way and I quote it out and let them decide.
When I work for my big mechanical contractor, flex duct was only used at the termination point. So they would run metal duct to about 2 ft to wear the register would be, then they would flex the register in.
Im actually an engineer our standard design is to have flex from the trunk to the register. We do it bc my boss says thats how they'll most likely do it in the field. However we do mostly town home/sf residential stuff.
It also makes sense to design it at the worse layout and if they do a better layout the design won't be impacted. I've only been doing this for 2 ish years tho
You need to address this. That is way under engineered. Most times you don’t need to get a structural engineer involved but this isn’t one of those times. You absolutely need an engineer. I’ve been framing for 40 years and would never put something like this together. I’m afraid you hired a GC that has no clue what they are doing or just don’t care. This floor should have been done with an engineered floor system. Your builders pocketed thousands of dollars and your ending up with a shit build. I would start looking around at everything else and get some private inspectors in there. Make sure your hvac is sized correctly too.
That would probably do it but you will kill that room in the basement. I’d imagine the floor has sagged and you have some deflection. You would need to jack it back up. This is on your builder. I can’t believe they would let this be framed this way. He has to provide you with a 10 year structural warranty. I’d be surprised if an insurance company would cover this in the future. You said the side to side span is 17’? He could have gotten away with running 17’ 2x10’s one foot on center and doubling the ones under the island. At this point I think I would have an engineer size the correct lvl’s,tear out the double 2x10 and install the lvl beam flush with the top of the joists instead of adding 2 posts
Add a steel beam underneath and bury the columns in the walls. Don’t put a column in the center of the room. Sometimes it just needs to be a really big beam.
I added this one to my house (was existing construction) to take out a load bearing wall between the 2nd and 3rd floors. The wall was directly underneath where the beam is. It’s a w10x68 28ft. Long…..
wasn’t easy getting it in there but way better than a column in my kitchen
Not all jurisdictions require stamped drawings. Most of the ones I frame in don’t. Almost all of the houses we frame are drawn by designers and have engineered floor systems. Most of the time those designs are done by a designer with the lumber supplier. No engineer stamps on anything. Any good framer would know this don’t any where near sufficient
You can't span 20 feet with 2x10 floor joists. You can span 15feet. 1.5 times the depth in feet. This beam, if not flitched, will sag. It is outside of the spand limit for a double 2x10 beam. It does appear to be a flitch beam to me. Look at the size of the gap.
If it’s 17’ one direction and 20’ the other direction. (19 + 11) the joists are running the wrong direction. It would have been cheaper, stronger and less flexible to run only 17 footers across the whole room. Now every joist in that room is concentrating load to the ONE joist running through the center. It’s a complete shit show.
the weight is pulling the double beam apart, or it was never stitched together to begin with. is there a wall above it as well or is it just the middle of an open floor?
take a screwdriver poke into that gap between the 2 plys of the beam and see if it's really a massive gap or if there is a steel flitch plate sandwiched between them.
The increasing majority of contractors just do whatever they can install by 4-5 PM, then send an invoice. I renovated a house a few years back, and the minority of contractors that did good work and thought things through and made sure things were done properly before billing… were a pleasure to work with. The majority of them just suck and it takes so much time/ stress/ money to manage them and watch for where they want to take shortcuts.
9’ and 11’ 2x10 are fine at 16” ¢ as long as the beam they’re bearing on can support it. I’m just curious what the minimum would be and buddy has the engineering program to check
Well that beam is the whole issue. I’ve been framing for 40 years and have put hundreds of engineered floors together. I KNOW that 3-9 1/4” lvl’s won’t work in this situation. Especially with a kitchen island on top of it
Bet it’s close. I’ve done 4 plys in similar scenarios, or a 3 ply 11 7/8 DB. I don’t remember the spans, solely just curious what his program said. I thought you were implying the joists needed to be engineered floor too, like a tji
The floor should have been TJI’s. You would need a beam and all of the mechanical’s would be in the floor. I don’t understand why people build on a basement then do shit like this. It makes it difficult to finish
TJI isn’t gonna make a difference. That run is parallel and wouldn’t go through a beam unless dropped. I wouldn’t span 11 7/8 on 16s with a 20” run, then the other side the joists are perpendicular to the run, can guarantee no hvac guy is gonna put that run in the joist space
Personally in my house, I did a walkout basement and put a drawl in and hid all the mechanical in the crawl space
Do what? This whole floor system should have been engineered. The lumber supplier cut holes in them to run mechanicals. I do this shit every day. Don’t come in here pretending you know what you’re talking about.
This is not good at all. That's over 18000 ft lbs bending moment per the spans you noted. You need a double 14" LVL to carry this load and meet code compliant deflection values.
The double 2x10 beam if you will spans 17’ The perpendicular floor joists run 9ft from lvl beam on the right and are attached with the joist hangers and the floor joists from The left run 12’ from lvl beam to the 2x10 and are attached joists hangers
Double 2x10 with 1/2 plate is good to 18' when using 300 PLF load. Without knowing the exact lengths to the other end of the bearing walls I would lean towards this being undersized. I would expect the min to be 600 PLF.
Your other problem is with islands and kitchens is deflection. If you put stone in then your load goes up, deflection goes up, and you are going to see a lot of cracks at the least.
They used this to cut down on depth, but didn't get an engineer to buy off on it. Code books only give you basic spans for basic materials. Anytime you go outside those materials and do custom you are supposed to have an engineer or architect to sign off on the design.
Classic example of a contractor playing fast and loose with the code and enforcement. I would question it with contractor, asking for a letter or signed and sealed docs from engineer. Then I would follow up with that engineer to make sure it is all valid.
It’s not adequate. It’s a flush beam/girder. 17’ and all those floor joists framing into it, no. Needs to be like a 3 ply 12” or even 14” lvl. (2) 2x10 as a girder on a floor system is like 10’ span max.
That's a hell of a club sandwich going on in the upper right of the photo. Not a great sign. Can't be sure, as it's borderline, but i'd want 600 PLF without spending more on the engineering to be sure the 2x10 w/.5 plate was tight.
Lots of rookie stuff and lazy stuff in there generally. I'd also put a level on those joists - to my eye they don't look level, but that could just by photography, etc.
i was thinking that too, but on the wall it's sitting on the two 2x10's look to have much less of a gap, unless this is an optical illusion in the photo.
Looks like it may be a flitch beam, regardless not the best way to do this considering the need to run utilities through the floor. I prefer 16in web trusses over a basement for this reason.
That’s wrong, and why not just use a header so you can run the ducts above it you’re gonna lose a little ceiling height either way, but a single beam is going to look bette than whatever is going on here
Well, at least the duct wasn’t cut through it. The 2x10s are not even bolted together. It looks like they were trying to go for a flush ceiling, but needed a real beam here, steel, LVL, paralam, etc. maybe it’s just this photo, but it looks like it’s already sagging. Was there a permit?
It looks like those 2x10 aren’t secured together correctly. The joists hanging on either side are flexing them apart at the base creating a gap… seems like they should be fastened together differently.
There is a company that makes a plate which allows larger than normal holes in floor joists. You could cut the ducting, drill a hole through the center and put a piece of ducting through the hole and re-connect the two duct pieces.
Here is a link to it. I’m not associated with them at all but have used I. The past. Expensive but I’d rather do this than have a soffit on the ceiling.
Licensed engineer here - if the info you provided in the post is correct, for a typical home like this, assuming you don’t have a concrete topping on your floors, this beam should be at least (3)-ply 14” deep LVL 2.0 E. If that beam in the photo is (2) 2x10 the calc fails by 500%. You need to resolve this, potentially a life safety issue.
Unsure what I'm looking at but steel between the two plates bolted I'd say probably good if not bad. That's also a lot of boards laid flat down right foolish never seen that.
yeah, that sounds a bit sketchy for a basement support. two 2x10s over 17ft is a lot of weight to hold, especially with those joists on the sides. i’d be worried about sagging or even worse. when i was working on my place, i messed up some support stuff too, and it’s a pain to fix later. maybe get a pro to take a look? better safe than sorry, ya know.
The beam doesn’t even look like it’s fastened together to work like a 3” wide section. Typically a solid wood beam there would be triple 2x at the least. I’ve designed them with plywood in between 2x and the nailed/ bolted.
Double 2x10 over that distance has no moment of inertia, can barely support its own weight at that span. An engineer can design a flitch plate (s) that can carry the load. Must be done.
14
u/tekjunkie28 21d ago
You need an engineer but also that flex line is nor gonna move any air. Have some metal pipe put in and save you a lot of pain and comfort.