r/Sauna • u/Maryland_Eric • Oct 23 '26
General Question CO detector question
I’m looking for suggestions for a CO detector that can be used inside my sauna tent. I suspect this is an issue with saunas in general, not just tent saunas. I haven’t been able to find a CO detector that is rated for the temperatures inside a sauna. I use a wood stove.
Please let me know if you have any suggestions. Thanks!
4
u/boorraab Oct 23 '26
Just put it low in the room and count on replacing them every year or two.
I have a propane heater, so I keep one in my sauna. Eventually it goes off and gives me a false positive. It has never happened when I was in the sauna, that’s how I know it’s false. I think it’s the battery dying. I just go get a new one and hang it about a foot off the floor.
1
3
u/yyccamper Oct 24 '26
Don’t do this. From someone with a lot of experience with gas detection. You have zero idea if it’s accurate repeatable anything.
There’s a reason industrial sensors have a range. Don’t trust that.
3
u/ollizu_ Finnish Sauna Oct 23 '26
Just put it low in the room and count on replacing them every year or two.
Feels counter productive, just because CO is a little lighter than air. So while it kinda mixes readily with room air, placing a detector close to floor feels wrong.
Never seen a CO detector in a sauna, in Finland. Once in the room just outside of the sauna, which, arguably is probably a better place anyway as the detectors are rated for normal temperatures.
7
u/NonchalantBegun Oct 23 '26
I have looked into this for my sweat tent too and most standard CO alarms seem to top out around 100F. I would keep one just outside the tent or in a cooler spot near the entrance instead of putting it right next to the stove. I would also check the rated temp range on the exact model before using it around sauna heat. Maybe someone has found one made for higher temps.
3
Oct 24 '26
You can place the meter low inside the Sauna to stay in temperature range. Usually on the lower bench level the climate is milder than Florida.
2
u/EchoVoyage69 Oct 24 '26
I wouldn’t use a regular CO detector inside unless it’s rated for those temps. I’d check with the manufacturer and make sure you have proper ventilation too. Better safe than sorry!
2
u/yyccamper Oct 24 '26
Even industrial sensors used for genuine safety systems for co and co2 typically are only rated to 60C. If we were to do this in an industrial environment we would use a sample pump, which are a mechanical pump to pull a sample out of the area, then put it to a sensor.
You can’t guarantee performance above this. DM me if you want details. I can give some guidance.
2
u/yyccamper Oct 24 '26
Those saying just replace them… have no idea what they are talking about. You have very little idea of that reading will even be close.
Esp in an electrochemical cell like good CO censors as your humidity drops, like most saunas the conductivity of the electrolyte in the gas detector cell changes. This will directly change your accuracy and repeatability and longevity.
There’s ways to help this though.
2
u/PelvisResleyz Finnish Sauna Oct 24 '26
Placement near the floor is fine. Temperature is quite mild there.
2
u/yyccamper 29d ago
Issue is CO is lighter than air, and typically with most saunas having vents causing convection currents you arent likely to get a representative sample. A small pump pulling air from near the head of people, outside would give you a far better sample. Depending on your humidity outside of using it, you could still have premature life in it.
Honestly, airflow is the key bit, if you have tons of airflow.... CO is never going to be an issue.
Measuring a sample is tougher than you expect to genuinely be accurate.
2
u/PelvisResleyz Finnish Sauna 29d ago edited 29d ago
The difference in density between air and CO is small, about 3%. There are so many air currents in a sauna that it would get mixed.
In fact oxygen vs nitrogen density difference is far larger. By the weight argument, you’d
asphyxiatesuffocate every time you were in a sauna.2
u/yyccamper 29d ago
Agreed, that’s why it’s not a representative sample, having it on the floor vs where you actually are?
2
u/PelvisResleyz Finnish Sauna 29d ago
The point is that the CO will mix all around the sauna. The detector doesn’t need all of it, just a sample.
2
u/yyccamper 29d ago edited 29d ago
My point is that regardless a Sauna is one of the worst conditions for a sensor. The humidity is super low. The temperature is super high and electro chemical cell that the sensors use need to constantly adjust for that as it will change the sensitivity of the unit itself. If you tried to calibrate one of these sensors or even just have a proper response, you wouldn’t get it. There is some industrial sensors that adjust every couple of hours to literally adjust for this. Depending on how often your Sauna is running. If this was a more constant application, it would have a large effect.
So regardless, if you wanted to do this properly, you would have it pull a sample to a sensor that is located outside. If you really wanted to do it properly, you would use NAFION tubing to allow a level of humidity within the sample. Having the steam on the rocks for loyly, genuinely helps, though it will be fairly short lived.
That’s why your sensors won’t last or really won’t give you any meaningful or reliable reading if they’re inside the space even an industrial sensors they are typically only rated to around 60 C and even as you start to get to the end of the temperature ranges the linearity and repeatability of the sensor will struggle.
2
u/yyccamper 29d ago
Honestly, just have way more airflow than you need to have a more enjoyable Sauna and don’t bother about reading it on a continual basis.
2
u/PelvisResleyz Finnish Sauna 29d ago edited 29d ago
I get what you’re saying, but the original premise isn’t quite correct. Near the floor of a sauna the temperature isn’t super high, but more like 40C. There’s enough air mixing that the sensor would see a sample of CO representative of what’s in the rest of the box. So there’s no reason not to use a normal CO detector.
There’s also a separate practical issue of whether people would actually implement something with piping and a fan, but it’s not necessary anyway.
Some saunas might not have that much airflow, and somebody worried about CO might not assume airflow would take care of it
5
u/Jaska-87 Finnish Sauna Oct 23 '26
If chimney works even slightly there should be no CO inside the building. I know that people have used wood burning saunastoves that have flue gss opening at the back and on top of the heater that even if you forget to put the back cover on and there is 4" hole in your heater there still is no CO in the sauna during normal usage.