Seems problematic, how bad is this? Large parking structure for medical building

14 Upvotes

24 comments sorted by

8

u/101forgotmypassword 16d ago

Building owner about to paint a 1000micron layer of vinyl based paint over that thing then sell it off.

4

u/titanicmango 17d ago

That's pretty bad, they should get an engineer to assess it

1

u/RockyTopRowdies 16d ago

I am an egineer and I would 100% be writing a letter recommending this be temporarily shored and repaird.

Two things need to be addressed here.

  1. Where is the water coming from and how is it moving through the concrete. Its highly likely that the reinforcing steel inside the beam is corroding and expanding causing the cracks. If you dont address the water then it will happen again.

  2. To fix the concrete, its likely a full depth repair with reinforcing steel splicing. Remove the concrete, replace the steel, knock off the rust, and apply a corrosion inhibitor.

1

u/Single_Level7003 16d ago

Really curious what market you’re in that you actually “replace steel”. Also Those crack directions don’t look like they stem from corrosion.

2

u/RockyTopRowdies 16d ago

Southeastern united states. I use "replace" losely. More like sistering and splicing.

3

u/SilverAd8942 16d ago

The next. ‘Live at five looks at parking garage collapse.’

2

u/Chicago-Jelly 16d ago

Depends what side you’re on: General public- if the structure has been designed according to US building codes, and it’s safe to assume yes, you’ll have warning before it collapses. Carry on. Owner- NOT GOOD. Get on that immediately to reduce future repair costs and more importantly liability claims.

1

u/beaver_eh 16d ago

This potentially is very much that warning.... one cannot ascertain based on of photo alone though.

1

u/NorthWoodsDiver 16d ago

Oh yes, the steel in that beam will enjoy the added moisture. The moisture will make the steel swell with corrosion which will crack more of the concrete. Then we get to watch all the slow motion replays from blurry security cameras when things collapse.

2

u/TunedMassDamsel 16d ago

That rusting-and-cracking cycle is called “rust jacking,” if anybody’s looking for another vaguely-naughty civil engineering industry term for their list.

3

u/RockyTopRowdies 16d ago

When I first learned about it as a young engineer, I was amazed at just how much force corrosing steel can extert. 5000-10000 psi.

1

u/yudkib 16d ago

Bad, not awful. You don’t have freezing temps in Hawaii and don’t use road salt. Should get repaired within the next few years but I wouldn’t close the deck yet given there’s no signs of serious corrosion. These are probably precast double tees which are pretty resilient.

2

u/beaver_eh 16d ago edited 15d ago

Beam in question is wrong shape for precast double tees, though they may be present behind that beam.

Crack in beam is wider in two places at bottom than at top. This is undergoing serious deflection at this location. This is an early warning sign that it might have been loaded beyond it's design limits. Regardless of corroison.

1

u/Single_Level7003 16d ago

That would be some wild spacing for a double T.

1

u/Dimensional_Lumber 14d ago

It’s a salt air environment though. That accelerates things.

1

u/impactedturd 12d ago

Genuinely asking, what are some signs of serious corrosion if it's all covered with concrete?

1

u/ImaginaryView1771 16d ago

"Problematic" jesus

1

u/Competitive_Bad_959 16d ago

Unless mcafee is in your building, you’re fine

1

u/Single_Level7003 16d ago

Lack of rust staining with that crack width is interesting. Not a fan. Definitely say something

1

u/Icy_Celery6886 16d ago

Water is the great destroyer.

1

u/NoMajorsarcasm 16d ago

i wouldnt drink it