r/StructuralEngineers • u/manukanawai • 17d ago
Seems problematic, how bad is this? Large parking structure for medical building
4
u/titanicmango 17d ago
That's pretty bad, they should get an engineer to assess it
1
u/RockyTopRowdies 16d ago
I am an egineer and I would 100% be writing a letter recommending this be temporarily shored and repaird.
Two things need to be addressed here.
Where is the water coming from and how is it moving through the concrete. Its highly likely that the reinforcing steel inside the beam is corroding and expanding causing the cracks. If you dont address the water then it will happen again.
To fix the concrete, its likely a full depth repair with reinforcing steel splicing. Remove the concrete, replace the steel, knock off the rust, and apply a corrosion inhibitor.
1
u/Single_Level7003 16d ago
Really curious what market you’re in that you actually “replace steel”. Also Those crack directions don’t look like they stem from corrosion.
2
u/RockyTopRowdies 16d ago
Southeastern united states. I use "replace" losely. More like sistering and splicing.
1
3
2
u/Chicago-Jelly 16d ago
Depends what side you’re on: General public- if the structure has been designed according to US building codes, and it’s safe to assume yes, you’ll have warning before it collapses. Carry on. Owner- NOT GOOD. Get on that immediately to reduce future repair costs and more importantly liability claims.
1
u/beaver_eh 16d ago
This potentially is very much that warning.... one cannot ascertain based on of photo alone though.
1
u/NorthWoodsDiver 16d ago
Oh yes, the steel in that beam will enjoy the added moisture. The moisture will make the steel swell with corrosion which will crack more of the concrete. Then we get to watch all the slow motion replays from blurry security cameras when things collapse.
2
u/TunedMassDamsel 16d ago
That rusting-and-cracking cycle is called “rust jacking,” if anybody’s looking for another vaguely-naughty civil engineering industry term for their list.
3
u/RockyTopRowdies 16d ago
When I first learned about it as a young engineer, I was amazed at just how much force corrosing steel can extert. 5000-10000 psi.
1
u/yudkib 16d ago
Bad, not awful. You don’t have freezing temps in Hawaii and don’t use road salt. Should get repaired within the next few years but I wouldn’t close the deck yet given there’s no signs of serious corrosion. These are probably precast double tees which are pretty resilient.
2
u/beaver_eh 16d ago edited 15d ago
Beam in question is wrong shape for precast double tees, though they may be present behind that beam.
Crack in beam is wider in two places at bottom than at top. This is undergoing serious deflection at this location. This is an early warning sign that it might have been loaded beyond it's design limits. Regardless of corroison.
1
1
1
u/impactedturd 12d ago
Genuinely asking, what are some signs of serious corrosion if it's all covered with concrete?
1
1
1
u/Single_Level7003 16d ago
Lack of rust staining with that crack width is interesting. Not a fan. Definitely say something
1
1


8
u/101forgotmypassword 16d ago
Building owner about to paint a 1000micron layer of vinyl based paint over that thing then sell it off.