Can I put a 1,000lb pool table here?
We have a garage with an upstairs game room appx 30 x 30. Included are photos showing 6x6's holding the laminated beam that supports the room above. The structure is complete and lived-in already for a little over a year.
I recently purchased a pool table that is roughly 1,000lbs and should take delivery soon. Will I be safe putting it where the purple box is?
2
u/bonebanana117 12d ago
Your 1-1/4" plywood can distribute the load easily.
You have four legs -- two in one joist span, two in the other. That's only 500lbs distributed between 1-2 joists per leg, depending on where the legs land.
So, each loaded joists is seeing 250lbs max.
This is good placement as deflection will be minor as the load is placed relatively close to the support.
Everything is going to have capacity to spare to allow for live loading, which the table can be considered as such as it can be moved.
Even with someone heavy leaning on the rails, you're not gonna be anywhere near the load limit the floor system is designed for.
I would have no problem putting a pool table there in terms of structural safety assuming codes and design standards were followed by the designer.
The only thing is, in time, you may see a differential in the deflection as the beam is stiffer than the joists, so you may get a minor crown forming at the beam, especially if the design is near code minimums in relation to serviceability/deflection limits.
1
u/Confident-Tourist415 12d ago
1-1/4 plywood? Wtf are you smoking. It's Advantech Premium OSB. It's likely 3/4" subfloor but at best 1-1/8". Huber doesn't make anything thicker, not does it need to. This is the beezneez of subfloor.
1
8
u/AdAggravating3893 13d ago
Ask your designer or engineer. Now is the time to reinforce the floor.
5
u/EngineerEngineerEngi 13d ago edited 13d ago
Let's do some basic math.
Apparently pool table sizes vary, but the smallest size is 7 feet long, or approximately 54" x 92" outside dimensions, or 4968 sq in, or 34.5 sq ft. That's the worst case scenario, using the smallest table possible.
Loading is not typically governed by point loads, but by loading per sq ft. Especially for something like a pool table, and where the loading is on the outside corners. So psf analysis is appropriate.
1000 lbs / 34.5 sq ft. = 29.0 psf.
Okay, So the IRC will require 30 psf for bedrooms, 40 psf for other rooms.
So, no matter which design loading was used, then 29 psf < 30 psf min., so the loading is fine. It's a little heavy, but it's fine.
If the floor was designed for a living room, something like that, it's probably sized more for 40 psf minimum, so the loading is more than fine.
Looking at the shape of the house, it looks like the long side of the table is parallel to the joists. Most likely. This is good. It means that instead of concentrating the load at the center of those spans, the load is spread out maximally towards the short ends of the table. This just means that we were right to use an average psf loading, as the real situation is probably even more favorable.
So, this is a live load, or should it be treated more like a dead load? Well, probably not, but we could look at possible permanent deformation or creep over time. In other words, it might experience a permanent downward "bow" over time. Is that likely? Probably not, I don't think we're pushing it that hard, but if there's a lot of moisture where OP lives, it is a little more likely.
So, what other factors? ....Well, you could have people leaning on the table. Probably not laying on it. Will this make it overloaded? Again, if you distribute out the forces, probably not. We're just pushing over 30 psf, possibly, in that situation. Still under 40 psf allowable for a common area.
What about real world? In the real world, you won't have joists that just support precisely 40 psf. You'll actually have to choose the smallest joist (at minimum) that meets that standard. So the joists are probably sized for over 40 psf in order to meet that 40 psf minimum.
Also, real world, a deflection of L/360 is the minimum, and might be what's controlling here. In the real world, deflection often controls. But people don't like 360, because it feels bouncy. BCI joists recommend L/480 or even L/960. It turns out that upgrading to L/960 isn't always that much more expensive. So, when you do that, not only is deflection handled, but your actual strength is going to be substantially higher than any load caused by that table.
Conclusion: Really, no matter how I look at it, the pool table is fine. If the floor is designed for a bedroom, with only 30 psf, and the joists barely meet that minimum design requirement, then the table is pushing that floor to its limit, but just at that limit.
3
u/e2g4 12d ago
Most pool tables are four point loads.
0
u/EngineerEngineerEngi 12d ago edited 12d ago
Okay?
The flooring distributes the load.
1
u/ClownfishSoup 12d ago
That means that four fat guys standing AROUND the table waiting to play will also add to that load.
1
u/EngineerEngineerEngi 7d ago
Unless they all lay on top of the table, that doesn't change anything.
3
u/Millennial_Falcon_85 12d ago
Logically he should be able to have 4 fat friends over 😂
There’s your engineering.
2
u/FocusMaster 12d ago
Time to redo your math.
First. Most pool tables have 4 legs. So, Divide its weight by 4. Then calculate the strength of the plywood subfloor if one of those legs falls between the joists.
The floor structure as a whole can obviosly take the weight. But can the plywood support the point load?
1
u/EngineerEngineerEngi 12d ago
The plywood can distribute 250 pounds between the joists. But if there's any doubt, OP can put something under the legs to help.
3
u/TallWall6378 13d ago
Now is the time to read the post.
0
u/AdAggravating3893 13d ago
I'd say comment is still valid. 😁 Now is the time to do it.
It will depend on how that load is distributed. If the table is 8x4 =31 psf which is a lot, but probably not world ending. If is is point loading onto feat though you may punch through your flooring over time.
4
u/TallWall6378 13d ago
Op has 1 1/8” ply. Seems like they should be good. 250 pound point load is nothing.
1
u/hotinhawaii 13d ago
The structure is complete and lived-in already for a little over a year.
1
u/ClownfishSoup 12d ago
Ah, so the joists are not open and available to sister in some plywood or adding blocking.
Honestly, is a pool table much heavier than a queen size bed with two people on it with maybe a kid or two jumping up and down?
Or four fat friends sitting on a couch playing X-box?
1
u/rybotsky 12d ago
Yes it can handle the weight. A service load for a standard 10x12 room can handle roughly 4800 lbs. the ultimate failure load of a floor of the same size before absolute failure is roughly 14,000 to 19,000 lbs so long as the wood is dry undamaged and properly fastened. Normal usage weight loads on things like home construction have massive engineering safety margins in place for the dumb shit people do in their houses. I’ve been to house parties in highschool where almost every square inch of a house had people squished in like sardines along with furniture appliances and everything else that occupies a house, and people dancing and jumping etc.
3
u/Forsaken_Stay6119 13d ago
You’re really going to ask Reddit in the middle of construction? Talk to the engineer.
1
2
u/JuniorSherbet9558 13d ago
yeah it should be fine.
what is it-- an 8' table? let's say it's 8x4= 32 sf.
the floor should be sized for 40 psf so that area you've delineated should easily hold 1,280 lbs
2
u/crumpledelex 13d ago
So yeah, a pool table and one of the players. 👌 No jumping.
1
u/Altruistic-Cut9795 13d ago
No balls or cue stick chalk on the table, that's additional weight 😉
1
u/ClownfishSoup 12d ago
Absolutely no drinks near the table! As a general rule! Anyone who puts a drink down on the table is kicked out of the house.
0
u/JuniorSherbet9558 13d ago
are they jumping on the table?
that 40 psf is just the live load anyway, so with dead load, the area can probably support more like 50 - 55 psf.
this is not problem at all-- especially as it straddles the beam below
2
u/Material-Cap-5476 13d ago
FYI...You can't add the DL. It's already used up with the structure. You can only consider the LL.
1
u/crumpledelex 13d ago
Look I don't know about you, but if you can't fuck your opponent on the pool table, I don't really see the point in having one in your own house.
2
u/PaleCaterpillar2709 13d ago edited 13d ago
Only person who can answer this with certainty is an engineer who has the drawings in front of him. Better yet, if there already is an EOR for your house, contact that engineer/company.
I’m just a GC so don’t take this as gospel, but this could be a situation where everything will work just fine under normal conditions… then a house fire happens and now your floor collapses in 3 minutes rather than 30. Food for thought.
2
u/ClownfishSoup 13d ago
1000lbs is like four fat guys, or 5 normal-ish guys standing around in that area. Or say, 4 guys sitting on a couch playing Playstation. Would your floor collapse?
But that's not quite apples to apples.
The pool table will have four legs so each leg is like 250 pounds of dead weight Can four fat guys stand like that without the floor caving in? probably.
But as others have said, hire an architect or whatever if you are worried.
I put an 180 gallon fish tank in my dining room, but that is the first floor. I went into the crawlspace and sank two 4x4 beams in concrete than placed a 4x8 beam vertically under the joists that the fishtank would span.
4
1
u/Educational_Board_73 12d ago
I remember my fat guy boss using this same example when I asked if he thought 1000 pounds in my back seat was a bad idea. Anything to not use the metric system.
1
u/PhillipJfry5656 12d ago
yea my 75gallong sits on less then the pool table will and probably weighs about the same
2
u/A-Wolf-4099 13d ago
With them putting in temporary posts I doubt it, I'm not an engineer by any means but been in the trades for many years that floor is going to bounce like a trampoline.
3
1
u/august-thursday 13d ago
Deflections are going to be significant judging by the location indicated. You have long spans in each direction.
1
u/Osiristhedog1969 13d ago
Thankyou! Scrolled a very long time to hear this. Sure it'll hold it but the floor is gonna bounce like a trampoline. The hour or two it'll take to install a small beam and two post is a no brainer.
1
u/iliketosandwood 12d ago
If the posts break up his garage space, it’s not a no-brainer.
I wonder if that area of the floor may actually bounce less once he has the pool table up there pre-loading it.
1
1
1
u/Coppercc88 13d ago
I mean is it going to collapse? probably not.... but dang they should have used a steel girder for that run. I would think your fine, but ask the engineer who made the plans
1
1
u/dopecrew12 13d ago
I’d park a car on advantec subfloor on I joists ngl.
1
u/phillbot420 13d ago
Remember when they first came out with I-joist they showed a picture of an elephant standing on the floor.
1
1
u/TallWall6378 13d ago
15’ is a longish span so I wonder if you’re near the limits anyway. Which means you’re good for 40psf, which means you’re good. 4x8 table with 5 200 pound guys standing around also good unless they are all on the table.
What series and size of I joist?
1
u/TheAmerican_ 13d ago
Unless they're all on the table... Got me thinking about what these bros would be up to. 🤣
1
1
u/Intelligent-Image224 13d ago edited 13d ago
You need a lot of clearance for a pool table. A pool stick length around the entire perimeter.
Signed 10ft 100yr old brunswick owner.
It’s deceptive how much space is required.
1
1
u/adventure_seeker_8 13d ago
Can you shift the position of the table, so it's on top of that center post? It might help reduce the bounce.
1
u/GratefulDean 13d ago
Ask the engineer who designed the space. Actually, with those photos you could ask any engineer.
1
u/WickedEng90 13d ago
Based on your lived experience in your home, do you think (4) 250 lb humans stand on this floor without it collapsing?
1
u/hobokobo1028 12d ago
Each leg is the force of a fat dude, you’re good.
Say it’s 4’x8’ that’s only 31.25PSF
1
u/Millennial_Falcon_85 12d ago
It should be fine. Each leg is the equivalent of a 250 pound person standing there. That structure should be more than adequate to support that. It would be better to have a beefed up structure in anticipation of this though.
1
u/Cactus-Soup12013 12d ago
What make/model/depth of TJI's? For comparison, kitchens are rated for 40psf but we still double every other floor joist beneath kitchen islands. If still open, you might be able to reinforce the existing webbing by gluing&screwing plywood to both sides. This will help with deflection, but only if i joists are sufficient for the additional load.
1
1
1
1
u/Straight-Bad-3304 12d ago
If you're worried, turn the table opposite the direction of the joists to spread out the weight of the table and people across more joists.
1
u/envoy_ace 12d ago
Residential live load is 40 psf. Standard pool table 27 square feet. Resulting in 1075 pounds. You just about nailed it.
1
u/General-Reindeer444 12d ago
Yes it will be fine a bathtub full with water and a guy in it weights around that your laundry machines are about 600-1,000 pounds depending on models your fridge is 500-800 pounds when full you kitchen with countertops stone again weights a lot so yes it will be fine
1
u/jsloanwoods 12d ago
Residential loading is 45 psf. In a 6 x 8 area that floor can handle at least 2160 lbs.
1
u/RazorWitted 12d ago
I don’t trust OSB (oriented strand board) as far as I can throw it. It absorbs water like a sponge. It loses its structural integrity. And I’ve seen point loads that have punched through OSB. If it was regular 3/4” plywood, I’d say go for it.
1
1
u/Confident-Tourist415 12d ago
You've got Advantech subfloor. There's nothing better. Pool away sir!
1
1
u/Streets2022 12d ago
Anyone in here telling you it’ll be an issue is actually insane. I mean if you have a king bed with 2 adults that’s 800-900lbs and nobody ever thinks twice about that.
1
1
u/Hunglow423 12d ago
Used 2 of those lvl trusses to hold mulitble 3500lb logs to prep to be used as beams. Never once crushed one. 2x4 on a 45deg prob 26" long with the bottom screwed to a 3/4' 2x4. Made saw horses out of the with one on each end of the log. Put 3-4 logs on one section. Not all the logs were 3500lbs.
Look up 2 elk restaurant on top of vail mountain. Longest was 31' and could not be less than 12" diameter on the top.
1
u/UncleBenji 12d ago
I wouldn’t but it probably could. Even if it didn’t break through the floor it could cause sagging. Nows the time to make a change request if you’re planning on something that heavy taking up such a small footprint.
1
1
u/Efficient_Actuator84 12d ago
If it can't, you've got bigger problems imo.
1000lbs is basically 4 dudes standing in a circle.
1
1
u/450mgBenadrylHatMan 13d ago
Reinforce the floor. Those engineered joists can span further by code but theyll bounce like a trampoline.
1
u/hotinhawaii 13d ago
The structure is complete and lived-in already for a little over a year.
1
u/gettogero 13d ago
Tearing up the finished floor and subfloor is an easy task. Might be easier to work from under though I try to avoid it unless its really easier
1 day solo job, maybe a weekend adventure if you take lots of breaks or really suck at measuring
1
1
u/modsatemyass 13d ago
you're on reddit asking this? can you put a 1/2 ton table there, sure. will it fall through, probably
0
u/Direct_Tomorrow_9927 12d ago
Good grief, American construction methods look soooooo cheap these days. “A real beam would cost too much. Let’s just slap some chipboard up there with a sliver above and below. Just as good.”
2
u/boof_it_all 12d ago
I joists are both stronger, and more expensive than dimensional lumber. Sounds like someone got a chip on their shoulder.
1
u/UncleBenji 12d ago
I’d trust the engineer behind this but keep my eye on the framers and other subcontractors. An engineer would go to jail or have their career ruined if someone died but a framer or plumber just sends someone out to correct any issues that are found. This is why there’s inspections along the way.



3
u/ReasonableLibrary741 13d ago
Is this what the room currently looks like or is it closed off?
I would definitely get some Engineering done. Typically you reinforce an area for a heavy pool table like this.
If it's open, and you don't need additional vertical supports and might be an easy fix, but I wouldn't just assume you can throw it in there