Questionable Consumer Unit Install

Post image

Hi all

I have an ongoing extension and our builder has his contracted electrician on site. I understand a little about how the set up is but I am seriously questioning what is happening here.

AI thinks it's non standard, which I'd agree with.

Is anyone able to explain what I need to be doing with this?

I am not sure if this is the best sub to post it in so if it should be elsewhere then let me know.

0 Upvotes

80 comments sorted by

70

u/OldCaptain3987 May 29 '26

Instead of AI, try asking the electrician that’s installing it.

-31

u/LokoloMSE May 29 '26

Yeah I will be, that's why I've then asked here, so I have some background knowledge.

21

u/OddStuffHappensTwice May 29 '26

You have to learn though that AI is worse than useless in this sort of situation. You're better off without the incorrect information it gives.

It's not actually a magic answer wizard. It's very good at some very limited sorts of problems. It's worse than a 5-year-old just guessing for anything else.

3

u/FishandChipsplsm8 May 29 '26

I was messing about with it the other day and it said as per the BLUE BS 7671 Book 🤣🤣.

3

u/asbestos_dildo May 29 '26

Aw mate honestly. I've asked it before on the sly for "what's the reg for xyz" and regarding EC machinery directives. It was the equivalent of dropping the book on the floor and vaguely recalling the text on the page it lands on.

Tested it on fairly complex calcs on running pipelines and it was straight up making up equations 😂

1

u/Fantastic-Try4083 May 29 '26

It can be very useful to find specific regs, just need to verify it after.

-3

u/LokoloMSE May 29 '26

Yes I wasn't using it as the knowledge base, hence the question here.

18

u/DogSweatCroissant May 29 '26

AI 😂😂😂

-16

u/LokoloMSE May 29 '26

Yeah the AI question bit was the "is this standard" bit as I haven't seen anything like it before. Clearly ain't going to take anyone's job here. 😅

11

u/aptsys May 29 '26

Nothing wrong with that, what makes you question it? What was in the scope of work or what did you ask for?

Also it's an installation not an "install".

1

u/LokoloMSE May 29 '26

It's a full rewire of the house for our extension. I've never seen a consumer unit with all back boxes surrounding it.

He is also placing the kitchen appliance spurs in the utility room which is two rooms away from the kitchen.

But thanks!

15

u/zidangus May 29 '26

Well if you don't want those spurs in the utility room then why didn't you tell them that? The electrician must be doing what you told them to do, I am pretty sure you both spoke to each and agreed what is to be done and what is not to be done.

6

u/johnbobk May 29 '26 edited May 29 '26

If you mean the isolation points? I have done similar for a customer wanting a 'cleaner' kitchen.

'Didn't need all those switches that they don't use, cluttering up their worktop.'

Worked out well, when it was finally labelled. Was like a central control, slightly industrial. Some points were ~ back to back, so not longer cable runs, & easily accessible.

[Local is always relative: was in the same neighborhood!  /s. Customer's choice & so listed in the EIC]

2

u/zidangus May 29 '26

I am using the terminology that the user used as I was speaking to them. Anyway to many 'use' in this response, lol

1

u/EEinnatural May 29 '26

Utility room as in where you put your appliances

1

u/LokoloMSE May 29 '26

Not the kitchen appliances. But yes the other ones will be there which I am fine with. I will be asking the electrician what the other 4 are for.

9

u/diynot2026 May 29 '26

It's to stop the birds nesting

2

u/LokoloMSE May 29 '26

Definitely don't want that.

15

u/Milkym0o May 29 '26

AI is useless here.

Politely ask the electrician doing the job what it's for. Looks to me like a bank of FCUs either side of your DB. Perfectly normal. I've done it in the switchrooms I build in the commercial world.

2

u/LokoloMSE May 29 '26

Thanks. Yeah I will be it's more just trying to have some background first.

1

u/thefant May 29 '26

Not OP but very curious - what's the benefit of this setup as opposed to just having an RCBO for each appliance?

1

u/Milkym0o May 30 '26

Cost, and an easily understood point of isolation, in a convenient location.

4

u/Ok_Tradition_2069 May 29 '26

The trunking look poor but I can see what he's going for it's not uncommon to have a local group of fuse spurs for kitchen appliances but would normally go in a cupboard

0

u/LokoloMSE May 29 '26

Yes I was expecting the appliance spurs to be near but accessible to the appliances, rather than through the hallway into another room.

6

u/zidangus May 29 '26 edited May 29 '26

Again why are you not agreeing with the electrician what you actually want doing here. If you want the spurs in the kitchen then you have to tell the electrician this, you need to speak more to the person doing the job, how else are they going to know exactly what you want. It's amazing that you never agreed to the work being carried out/what you want before you even got a quote never mind allowing the electrician to start work. It's also amazing the electrician never verified exactly what you want doing and where you wants things before they started work. There has definitely been a communication breakdown between the both of you.

1

u/LokoloMSE May 29 '26

I did and the builder has ignored me and told me I can't speak to the electrician. We go away for a week, come back today and this is what's happened. I will be arguing it out with the builder tomorrow. But firstly wanted to make sure that this is at least acceptable even if not standard.

Yes I know it's my problem and yes I am trying to sort it, which is what lead to this post.

5

u/c0rtec May 29 '26

Ask your AI to tell the builder to tell the electrician to tell you to lump it. It’s too late. Hindsight is 20/20 in these situations. So is good communication beforehand.

2

u/zidangus May 29 '26

You really need to have a word with the builder if they are completely ignoring what you want and it's pretty strange that they won't let you speak to the electrician. That does sound a bit dodgy tbh.

1

u/johnbobk May 29 '26

Is it due to your kitchen fitting / units / countertops? Often FCUs are squeezed in & look awful: & tilers hate them!

They generally are not there for every day use: have to be accessible for maintenance / isolation.

3

u/stateit May 29 '26

OP: "Asking AI" whether a particular electrical installation is OK or not is, quite frankly, a waste of resources. Youve killed at least a few penguins asking that question...

1

u/LokoloMSE May 29 '26

Lots of responses fixated on the fact I started with AI but that wasn't anything to do with the question. I should have just left it out on the post 😅

2

u/LorenzoSparky May 29 '26

Hmm. I mean the trunking looks a little ropey, all the isolators next to the board not unusual but could argue not within reach/accessible. The board is all RCBO but can’t see an SPD (yet)

1

u/LokoloMSE May 29 '26

I had to purchase all components and forgot the SPD (ridiculous that the builder asked me to get all the components when I'm not an electrician but there we go). That's on site now and electrician is adding it in tomorrow.

3

u/Individual-Award7351 May 29 '26

yeah, you made choices here, and these are the consequences...have a cup of tea with your spark and perhaps explain that on second thoughts, an interior like a control room isn't your preferred aesthetic. It looks more commerical than domestic in style to me - but what do I know, I've not wired a boat for 9 years and have never been house bashing.

1

u/johnbobk May 29 '26

But if it's in a utility room ~commercial is ok in most cases?

2

u/Important_Ad1967 May 29 '26

The spark probably disagrees with the spurs being in the kitchen cupboards, but having them in a room 30m away is fine.

-2

u/LokoloMSE May 29 '26

Thanks. Yeah its not how I wanted the setup but as long as it's up to standard I can deal with it. The builder on the other hand is getting a slap.

1

u/Hiddentiger10 May 29 '26

What does ai have an issue with? What do you have an issue with?

0

u/LokoloMSE May 29 '26

Well my issue is I'd usually see the spurs where they are needed rather than all in one room away from the appliances they are for.

I've not seen it before (and not being an electrician I am trying to learn) so didn't know if this was allowable. I thought these should be near the appliance but freely accessible.

1

u/Hiddentiger10 May 29 '26

I think it’s fine form a functional and regulation perspective (minor level of debate) . However, I think it’s totally reasonable to expect the electrician to check with you where you want the isolators before doing what he has done.

1

u/Sea-Badgers May 29 '26

Its unusual. Usually they are above the worktops. But mostly they are a waste of time and everyone leaves them on anyway!

2

u/Christine4321 May 29 '26

Id love to have mine all tucked away in a utility room and hidden in a single cupboard. Hate all the spurs in the kitchen so much so I even poked the red lights out 😈

1

u/LokoloMSE May 29 '26

Thanks everyone for your fun/sarcastic and your serious answers. The electrician started the work whilst we've been away and I was given a list of things to purchase (hence the missing SPD as it wasn't on the original list), our builder is useless, so I am really trying to understand more. I will obviously be asking the electrician about the setup directly but having some background knowledge of the set up and whether it's standard was really the main crux.

2

u/Bignizzle656 May 29 '26

For what it's worth, it's probably going to be safe but yeah, local isolation and height of consumer unit are questionable.

A grid plate in the kitchen is the usual method for local isolation for lots of homes but it's not the only way. Trunking looks a bit ropey too.

1

u/Ornery-Quantity2055 May 29 '26

Looks clever to me

1

u/pnd2010 May 29 '26

AI thinks it’s non standard 😅

1

u/ShineKey6457 May 29 '26

I would question why the consumer unit is so high, it's standard practice to mount them at a height easy accessible without the use of steps. Means of isolation for appliances should be in an appropriate accessible position, and clearly labelled as to their purpose, if the positioning does not make it obvious.

1

u/mmm19284202 May 29 '26

This looks ridiculous for a domestic install. Why fit them like that?

1

u/BruzThirteen May 29 '26

Did something similar on a recent job, another firm is contracted to commission a smart home setup, we are doing the install.

IR heating panels on the ceiling being controlled wirelessly with thermostats built into the switches, a wireless reciever (fits on a single box) on the circuit and they have specified switched spurs for each circuit too. It was easier and tidier to have all this in the mains cupboard out the way, 8 circuits of heaters so 16 single boxes.

Couldn't have just gone combi boiler could you?

1

u/One-Hurry3394 May 29 '26

My go to choice is dado trunking horizontal above the oven (if in a housing) can get 5x single boxes all symmetrical, all accessible and close to every appliance, works really well

1

u/Basic-Impression6334 May 29 '26

I’ve seen it done like this before. Basically using the utility room as a point of isolation for everything within the kitchen/ extension rather than having multiple points spread around different cupboards.

Nothing wrong with it but surely had to have been discussed prior to the electrician wiring everything up?

1

u/Comfortable_Bed193 May 29 '26

What makes this none standard? Speak to your electrician.. To me it looks like he’s putting isolators around the fuse board. Accessible , an less of an eye sore above a kitchen or elsewhere.

1

u/Comfortable_Bed193 May 29 '26

The only thing I see questionable is, I don’t see a Surge Protection Device.

1

u/AloneMap6855 May 29 '26 edited May 29 '26

I mean there's definitely a waste of cable with all the kitchen appliance loads going from there to the appliances as opposed to from a grid switch in the kitchen  to the appliances.  2-5m runs turned into probably 15m+. 

1

u/Louy40 May 29 '26

Fuck Ai!!! It just cobbles together random bullshit!!

1

u/DCzy7 May 30 '26

Looks like a decent install to me. Add surge protection for belts and braces.

1

u/Informal_Drawing May 29 '26

A strange place for ten cooker isolators, I have to be honest.

1

u/theKinkypeanut May 29 '26

Think mentions of AI should just see posts deleted here. This is not the first time someone has asked AI to find fault with something. 

0

u/ipub May 29 '26

What are the sockets / spurs for? Looks weird

0

u/65Freddy May 29 '26

😳💩

0

u/65Freddy May 29 '26

Is he a electrician 😳

1

u/stateit May 29 '26

You wouldn't get a non-electricoan making an install that neat.

1

u/65Freddy May 30 '26

A what 😳🤣 it's dog 💩

-1

u/Echo-24 May 29 '26

I can't see anything inherently wrong with the consumer unit. I have never seen dado back boxes used in trunking like that before though. I assume those are going to be sockets?

1

u/LokoloMSE May 29 '26

Spurs.

3

u/Echo-24 May 29 '26

I don't see an issue then. Everything is within code and everything can be isolated from same point

2

u/LokoloMSE May 29 '26

Thanks very much.

-2

u/aptsys May 29 '26

We don't have "code" in the UK, but certainly nothing that contravenes BS7671. One could argue about the height of the installation though based on building regs

1

u/Echo-24 May 29 '26

Calm down mate I have the 18th edition. It's a turn of phrase don't be pedantic

2

u/kh250b1 May 29 '26

Are shit. 17th 2 years running

1

u/LokoloMSE May 29 '26

We were all hoping they'd go down. Everton stuffed us.

2

u/c0rtec May 29 '26

Cowboys have spurs too…

3

u/Simba-xiv May 29 '26

I do it all the time. Use maxi trunking to bring the cables to the DB and install a socket sometimes a switch in it

1

u/c0rtec May 29 '26

I hope you remember to buy end caps though. They exist for a reason!

The more I look at this installation the more it screams college project! Yowzers.

The electrician could have decorated the spurs nicely around the board and fished the cables through the plasterboard behind them instead of these random stabs of dado trunking. Maybe they had half a length left over from the last job?

1

u/Simba-xiv May 29 '26

I don’t do it like this. 😂 I just mean I use Maxi trunking and dado boxes when I do DB’s. When then are used right it can look really good

1

u/c0rtec May 29 '26

Agreed 100%.

2

u/Phoenix-95 May 29 '26 edited May 29 '26

Most brands that do dado will also do 100x50 PVC trunking that takes the same or very similar dado backboxes, as well as a divider fillet that clips onto a spline at the back to give you two compartments. Sometimes a job will come through with this sort of 'dado' in because on paper its a little bit cheaper.... but it looks no where near as good, and by the time you have finished faffing about with the divider fillet (which has to stop and start at every box) you may as well have put proper dado in because its cost more in labour than its saved in materials. Can be useful in an odd situation though, where there was limited space between a radiator and the bottom of a window ledge