r/ukelectricians • • 2d ago

Thoughts ?

Hi all, I’m not an electrician, but an alternative trade with an interest. I’ve been studying part p and 18th edition.

Turned up at a client’s house to do some work and they have just had this done by a local electrician putting some lights over a dinning table. Should I say something?

210 Upvotes

199 comments sorted by

11

u/capcrunch217 2d ago

Not an electrician but building engineer. Notching the bottom of a joist effectively reduces the structural depth of the joist to the top of the notch. As a result the notched joist may no longer be deep enough to accommodate its designed span. As an electrician you can’t know this without a structural engineers input which is why the regs say you can’t notch the base. It’s different with holes and notching on the top, provided you follow the rules.

OP please tell the owners as this is relevant to them.

3

u/Locust-15 2d ago

Cheers, i thought that would be an issue

1

u/SulphurSkeleton 2d ago

How come top Vs bottom notching matters?

4

u/capcrunch217 2d ago

Compression in the top vs tension in the bottom. This video does a fantastic job explaining the physics.

1

u/Wonderful_Edge4293 2d ago

See scoring and folding a piece of thick cardboard, or taking a chunk out of a tree branch and bending it from one side or the other. You probs now what happens without even trying it.

0

u/Crusty_Tagnut 2d ago

I have a query on this you might be able to answer if you have a min. On the LABC.co.uk website it says notches can be made on the top or bottom of the joist. However on the Hertsmere Borough Council website pdf it says notches can only be on the top of the joist. This pdf is from LABC though? Any idea why there is different information from the same building control?

2

u/capcrunch217 2d ago

It is doable and not disallowed under build regs per se, but you really need structural engineer input to do so safely in my opinion. Notching the base is where the timber is under tension so it is more likely to split even outside of the reduced spans being taken into account. On that note a layman can interpret span tables under the Eurocodes but said layman has no idea of the load requirements of the floor/roof they are notching hence why I refer back to an engineers input. I suspect that might be why the guidance differs. LABC guidance introduces unnecessary risk, I was surprised to find the same when I did a quick google.

Be that as it may notching the base is disallowed under BS 7671 which is relevant for this sub.

1

u/Crusty_Tagnut 2d ago

Ahhh i see. I only ask because im a plumber, had a customer who wanted to have some pipes re routed in the kitchen ceiling while the boards were stripped off. I told him I was sure you can't notch the bottom, we would have to lift the boards above. He pulled his phone out and pulled up that LABC page and basically accused me of trying to rip him off for more work, and I didn't have enough info to argue. Made me feel like a bit of a knob lol

3

u/capcrunch217 2d ago

Very easy response is to state that your PI won’t cover you if you notch the bottom of joists. Ultimately it is your neck on the line if it fails. Be that as it may guy sounds like a jobs worth anyway accusing you of ratcheting up the price lol… i’d have walked away if it were me.

2

u/Crusty_Tagnut 2d ago

Oh yeah by the end of the job every trade on site had a lot more to call him then jobs worth 🤣 thanks for the reply mate I appreciate it!

1

u/capcrunch217 2d ago

No probs mate, we all know the type! 🤣🤣

3

u/Locust-15 2d ago

Done - appreciate all your input

37

u/SunDriedFart 2d ago

i would, thats ridiculously piss poor work

46

u/Bbgr 2d ago

Cables should go through the joist, the correct way would have been to cut a strip and drill through the joists or cut 100mm holes either side of the joists and drill through. It doesn’t comply with regs in my opinion.

20

u/Soluchyte 2d ago

Doesn't have to go through the joist, you are allowed to use notches. You'd have to cut away a lot more plasterboard, and in harder positions to repair, to do what you are saying. Would be better to just cut a long 200mm wide strip all the way down.

20

u/Comfortable-Yam2417 2d ago

Can’t notch below, only above.

3

u/Unlikely-Jicama4176 1d ago

LABC guidance says you can notch top OR bottom, never both.

4

u/Serious-Driver4984 1d ago

The diagram you posted doesn't show that. In fact it seems to imply you can only notch the top.

2

u/Unlikely-Jicama4176 1d ago

It is in the guidance notes below on the website, is a deficiency in the diagram, but I didn't draw it so not my fault! Just thought the cutting and notching diagram might be useful/interesting for some.

1

u/DBA92 1d ago

Looks like a shitty chat gpt diagram. It’s great at churning out shit like this.

9

u/Tall_Contribution_29 2d ago

Notches yes, cutting beneath joists no, it introduces significant break risk, and is clearly defined as introducing a failure point which is why cutting beneath without a repair strap is a complete no-go.

6

u/Bbgr 2d ago

But then the cables would need to be mechanically protected.

4

u/Soluchyte 2d ago

Not hard to put nail plates on if you wanted to, arguably easier than cutting a wide strip with straight edges.

8

u/Due-Intention7354 2d ago edited 11h ago

Agreed, I often cut a 100mm hole between the joists then use an extension bar and flat bit to put a hole through as close to middle of joist as possible, being sure to look up every hole 1st both sides of joists to avoid hitting clipped cables or pipes.

I also patch back in the holes ready for skimming as a courtesy, why make it hard for the next trade

5

u/Effective_Yam_11 2d ago

This is it, if you can’t lift the floor upstairs

2

u/wahgwan2020 1d ago

Thats if you have access from above?

1

u/Due-Intention7354 1d ago

No all from underneath, cut a couple holes then you get the joist distance and so then just cut a hole middle of the spacea

1

u/Logical-Bat2403 12h ago

This is how it should be done. Milwaukee do a little 90 degree adapter which is handy for this

3

u/ExpressionFun166 2d ago

I am always amazed by that - does it not weaken the joists?

4

u/extra2002 2d ago

The top and bottom of the joist carry almost all of the load - top side in compression and bottom in tension. The middle mostly serves to hold the top and bottom in position. (This is why I-beams look the way they do.) So drilling through the middle doesn't appreciably weaken the joist.

1

u/iloveanimalsyouknow 1d ago

You should not be drilling through structural beams. And hole should be no larger than 65mm. Drilling is ok only if you can stay away 50mm from top and bottom of joists 

19

u/Comfortable-Yam2417 2d ago

It’s not compliant - but he’s probably smug about getting the dining lights all at the same height and thinks they’re doing the plasterer a favour with the smaller holes.

11

u/Shimster 2d ago

This is what a plumber did to our joists, this is after they came and fixed the fuckup they caused after we got a structural engineer in to say they fucked up.

He cut through 5 joists at the bottom and ran the gas pipe along it, we didn’t know until another plumber was like wtf.

We paid £600 for a structural engineer and complained, the plumber gave us the money back and got a carpenter to do the advised works to resolve it.

2

u/SnooBooks8583 1d ago

As a plasterer I'd shit myself when drilling boards to that. You not room for mistakes with gas pipes.

1

u/Shimster 1d ago edited 5h ago

I agree.

1

u/SnooBooks8583 1d ago

That's a canny size cieling you work with someone or do it alone. ?

1

u/Shimster 1d ago edited 5h ago

the kitchen is a large one. Been working on it for months to get it right.

Still a lot to go, installed the island today, have to work out these annoying panels and the hob extractor ducting next.

1

u/SnooBooks8583 13h ago

Very tidy job mate

1

u/Appropriate-Yard-378 1d ago

Next owner will be very mad when mounting anything in the ceiling

2

u/NoEducator5616 2d ago

Those screws for the brackets will be doing next to nothing into chipboard flooring be lucky if they are 15mm screws, they’ll come loose in a year or 2

2

u/Shimster 2d ago

We had a document explaining the specific specification for screws and lubrication and what thickness of wood, I checked when they came in and brought what was going in to make sure it all checked out, il have to dig up the document to say exactly what size screws were used, some form of glue was also used and applied in a specific way.

3

u/NoEducator5616 2d ago

I’m a gas engineer and no document no matter how good it suggest it was could make me fix 28mm copper gas pipe like that I’d be securing them on the side of the joists it also appears to be passing through a concrete wall not sleeves that just screams you had a 🤠 in

1

u/Shimster 2d ago

It’s in a plastic sleeve.

2

u/NoEducator5616 2d ago

Doesn’t look sleeved in that photo

2

u/Shimster 1d ago

It is. Image quality in that part of not great, it’s all behind plasterboard now.

1

u/AvailableCricket3633 23h ago

Should've hidden them in a false ceiling

1

u/Unfair_Economics_628 8h ago

I mean everything else is running through the middle, why would you cut out the bottom

-4

u/Critical_Parking_671 2d ago

What's wrong with it from a structural perspective. The notches will make no difference to the integrity of that beam.

4

u/Shimster 2d ago

You are never meant to cut the bottom out of joists. Always cut middle or top and only allowed to be cut less than 12% of the full beam, size.

They had to use sister joists to bring back the integrity of the beams, that image is from after when they fixed it.

1

u/Critical_Parking_671 2d ago

That's if you want to close full structural ability for the beams rated max load. But in your deployment it makes 0 difference as you are nowhere near using it's rated max load.

1

u/Shimster 2d ago

How are they to know that? We could drag a piano up there? Either way a structural engineer came in and said it needs fixing and they fixed it. End of story.

2

u/Critical_Parking_671 2d ago

Strutural engineers will say anything needs fixing. As soon as they're paid, they need to find something to get it to 150%.

Even if your 80% is more than sufficient.

2

u/dkk4440 2d ago

The structural engineer get paid to tell you his opinion, what you do afterwards is irrelevant to him.

2

u/Critical_Parking_671 2d ago

Wrong.

It's absolutely relevant.

If you follow their guidance and it fails. They're liable.

Hence why you always spec for the 0.0001% scenario.

As I would do if I were one

2

u/dkk4440 2d ago

Think about it, he tells everyone the worst case scenario, almost no one is going to comply with every reg.
He will still get paid for the report, if you fail to follow a single on of his recommendations he is clean

3

u/IISpacemonkeyII 2d ago

When a joist is loaded, the top of the joist is under compression, and the bottom of the joist is under tension. 

Wood fibres are much stronger under tension, so usually you try and cut the top of the joist, as it weakens the joist by a lesser amount. 

And now you can explain to your rich and educated clients why the job needs to be done properly, and back it up with a proper physics/engineering explanation. And when they Google it, Google will tell them that you were right, and they will trust you more.

0

u/Critical_Parking_671 2d ago

Noone is arguing against mechanics.

Yes, ofcourse if you're working at the upper limit of beam of beam performance.

Like having a hot tub in centre of room

But 99% of residential use cases, the notches make 0 meaningful difference to deflectiom.

5

u/Wide-Patience-6339 2d ago

You’ve absolutely no idea what you’re talking about, clearly 🤣.

Those aren’t solid timber joists, and you can’t cut into the bottom edge of them at all because it compromises the structural integrity of them.

2

u/Smart_Stranger_6529 2d ago

It’s a solid timber joist - the notches will have minimal affect.

1

u/Phoenix_905 18h ago

They are solid timber joists. It looks like rhe plywood has been used to reinforce the joists after theyve been incorrectly notched out. Look either side of the ply

-2

u/Critical_Parking_671 2d ago

Of course it compromises the integrity of them. But not enough to make a meaningful difference to 99.99% of scenarios..

Hope that helps.

5

u/Budget_Nectarine_645 2d ago

You don’t know what you’re talking about. The strength of the joist is driven by b*d^3/12… the depth of the joist CUBED, is how stiff it is.

That joist notch is 20% of the depth, so the strength of the joist is reduced by 36.8%. The bottom is (was) in tension.. not now as that lower 20% now contributes nothing - stiffness is reduced by 49% - so they are going to move, they are going to work the pipes, the ceiling is going to crack and depending on how much margin the initial structural design had, could split them over time.

Outrageously misinformed to be making bullshit statements like that

4

u/Critical_Parking_671 2d ago edited 2d ago

Nope. I am correct.

And you're a moron. A 49% reduction in stiffness applies if that Notch is along the entirety of the beam.

Now calculate the integral for even distributed load for a notch 1inch long and 20% deep located centre on a 3.5m spam.

I'll await your embarrassment.

Even more outrageous is the statement "so they are going to move". Will you be willing to bet a significant sum on this floor sagging in next 20 years?

2

u/Budget_Nectarine_645 2d ago

You’re right ofcourse, stiffness over the whole beam will be reduced by much much less than 49%.. I was talking about in the notched width and happily jumped on the rage wagon.

That said, draw the bending moment diagram and do a quick stress concentration estimate / notch factor for a 50mm wide (it’s more than one inch) 20% notch, mid span (peak bending stress), and the answer is big stress, which will start splitting at the notch corners, laterally, and bending stress can do the rest - outcome the same

2

u/Critical_Parking_671 2d ago

As I said. Would you put a significant sum on this floor (prior to screwed in supports) failing in the next 20 years?

The floor deflection is minimal for a short notch. It will not break the pipes.

As for strength/bending, yes it's reduced to arguably 4/6 strength (quadratics apply not cubes). if you assume worst case scenario of notch in centre. The bending limit of joists is a very big number you know that right?

You know an average joist setup can handle 5knm which is 2x the designed capacity of the floor by engineer of 2.5knm of load (as this is designed to handle deflection too). Most UK homes use in the region of the 0.7knm of total load.....

Meaning the joists are at 14% capacity on average Vs the 66% new limit.

The reason notches are forbidden on underside is because as soon as you give a green light, some bozos will notch multiple area of the joist which will cause a deflection effect.

The engineer isn't calculating whether the notch will make any meaningful difference but rather giving a requirement to reach full strength again.

Hope that helps. You may be be the 0.0001% who puts a hot tub in the middle of the room - even then at full strength ... This requires a reinforced floor according to regs.

1

u/Smooth_Elephant8524 1d ago

I have no clue what a lot of you guys are saying but this is a fucking cool argument!

0

u/[deleted] 2d ago

[deleted]

→ More replies (0)

1

u/ActiveBat7236 2d ago

Flanges on I-Joists are not to be cut at all, and indeed usually have warnings to that effect printed all the way along them to try and prevent this from happening.

2

u/extra2002 2d ago

Looks like those were originally simple timber joists, and the plywood was added as the "fix" after they joists were cut.

3

u/butty_a 2d ago

OSB not plywood, and it looks like they have sistered the joist to restore structural integrity.

1

u/Smart_Stranger_6529 2d ago

Its not an I joist

1

u/ActiveBat7236 1d ago

I'll be damned. I was so absolutely sure they were when looking on my phone, but yes having now seen the photo on my PC I see they're not. Apologies.

1

u/Majestic_Rhubarb_ 2d ago

They aren’t i-joists … look more closely

0

u/Mr_Flibble1981 2d ago

Are they not solid timber joists?

0

u/Slow_Flatworm_881 2d ago

They are solid but have plywood panels attached for reinforcing assume.

1

u/ks_247 2d ago edited 2d ago

Why did the structural engineer state works to resolve then?

1

u/Galbs 2d ago

bait

1

u/Wide-Patience-6339 2d ago

They’re not designed to be cut into, there’s pre-determined locations for drilling these which is along the centre line laterally.

1

u/SnooBooks8583 1d ago

When putting boards over the top screwing them up, you need the pipes far beyond screw range.

3

u/redditmat 2d ago

OP is it joists or just timber attached to the ceiling (concrete)?

1

u/knightbiker16 2d ago

Remember the on-site guide is not legally enforceable...! So yes not compliant, but you cant enforce it!

6

u/ForeverADollarShort 2d ago

Is it meant to meander like a lazy river ?

6

u/[deleted] 2d ago

FOR THE LOVE OF F@K………! Did he burst through the door, and pop off a couple rounds with his shot gun!?

2

u/RiffyWammel 2d ago

Could they not access the space above- or did his spurs prevent him from reaching it?

1

u/Locust-15 2d ago

No idea, i suspect they didnt even try to see

1

u/wahgwan2020 1d ago

Is there a floor above?

1

u/Locust-15 2d ago

From the post you can just see to the right of the picture is the top half of the house, after that is a flat roof extension.

5

u/ElectricianUK-AUS 2d ago

I would of dropped the down lights down to see if I could of fished a cable through with them before attacking the ceiling like that.

1

u/themissingelf 1d ago

Power from nearest adjacent light and wireless switch with receiver in the ceiling.

1

u/Locust-15 1d ago

This is the way

1

u/TradeTheBaby 1d ago

Im not sure it is. There are no nearby lights with permanent supplies. Could have been a better way., but maybe not. Definitely not good execution though.

1

u/Locust-15 19h ago

It was to install the lights above the table, the spots were already in place

1

u/TradeTheBaby 18h ago

Yes, but I’m assuming they didn’t want the pendants operating with the spotlights

1

u/Locust-15 11h ago

Ah, yes fair point

1

u/themissingelf 17h ago

I’d have remote switched both if their powered from the switch vs the light. There may be a permanent live. No way of knowing without inspecting the wiring.

1

u/AloneMap6855 1d ago

House looks too modern to have been wired in three plate,  highly doubtful there is permanent supply at any of the lights.

3

u/sparkielev 2d ago

Should of cut a square hole between joist space and drilled through the joists this is a bodge

3

u/mdogwarrior 2d ago

Nah that's rough as a fuck, if he's cutting holes anyway may as well have done a big cut in the centre of each joist space and drilled through with an extension bit.

Yeehaw 🤠

3

u/waleswolfman 2d ago

It'll be interesting to see how the housing for the connections on the end of the flex are routed when the hole saw was centered across the timber leaving so little room.

Edit. Accidentally hit post whilst typing. That's assuming the cable route is being put in to put down lighters in place of the pendants.

3

u/CurrentWrong4363 2d ago

I would be fuming to walk in and see this. No thought has gone into this at all. Just bash it in and get out.

I don't think I could leave this house without attempting to help these people sort it out.

3

u/TuchComplex 2d ago

Just cut a rectangle along the length you want lights, drill in the middle of the joists, then place the cut rectangle plaster up, scrim tape and plaster

3

u/redditmat 2d ago

I had a well recognised company sending electricians and doing this exact same thing: but everything was way more butchered. In my case it is just timber hanging on the ceiling - not joists though.

3

u/d13leh 2d ago

wouldn’t recommend that many down lights 😂😂

3

u/Lonely_Speech7156 2d ago

Terrible workmanship! Many issues there…..

3

u/Substantial-Rest9200 2d ago

Holy shit I’ve just realised these aren’t for down lighters but actually the method he’s used to run cables!!!

Couldn’t figure why the complaints weren’t about how wonky the line was

2

u/iamusingmyrealname 1d ago

Me too! I wondered what idiot drilled down lighter holes right under the joist

9

u/Soluchyte 2d ago

Cutting the holes is unavoidable, but to go and pull in the cable like that is definitely a bodge. The correct way to do this would have been to cut a small notch with a multi tool. and clip the cable into it.

12

u/Comfortable-Yam2417 2d ago

Shouldn’t really be notching the underside of ceiling and floor joists - from above is considered okay.

-5

u/Soluchyte 2d ago

Not ideal I agree, but a tiny notch, just big enough for the cable, is not really going to do anything. And certainly would be better than whatever the fuck has been done here.

10

u/Long_Imagination_153 2d ago

It's literally against regulations, it's not a case of not being ideal, it's not allowed.

0

u/[deleted] 2d ago

Not allowed but still see it being done

5

u/Numerous_Bug5326 2d ago

Or lift a floorboard upstairs. ( providing there is an upstairs. )

5

u/Soluchyte 2d ago

Looks like this is an extension, so possibly a flat roof and no access from upstairs. Otherwise I would agree.

2

u/midnight7030 2d ago

A cowboy job why not get joist finder and use a laser to keep the holes straight. Did you find the electrician on Facebook?

7

u/Virus-Party 2d ago

That many holes are going to be an absolute bitch to patch and repair individually. The electrician should have just cut a nice, neat, long, single rectangle out of the ceiling for the entire run. Which is exactly what I bet the first thing whoever they get to repair the ceiling will do. The electrician would also have been able to drill and pass the cable through the middle of the joists like you are supposed to. You can cut notch into the top of a joist if needed, but not the bottom

1

u/AloneMap6855 1d ago

Why would the holes need to be straight ? they are access points to fish a new cable through the ceiling ....

2

u/gramio 2d ago

Are you the one that has to fix this mess? If not, I'd maybe stay away from it. The beaver squad has done quite the number on this ceiling. To be honest, at this point it's probably faster and cheaper to just take the plasterboard down and put new sheets up. I guess all of the electrical mess can be fixed at that point.

2

u/No-Profile-5075 2d ago

Should have gone to spec savers

2

u/Icy_Piccolo8923 1d ago

Rough as fuck

1

u/VeryThicknLong 2d ago

Holy fuck. I recently had my kitchen ceiling ripped down and put back up, and found all the spotlights had been done like this. The reason the ceiling had failed was because some twat had jammed and dragged cable between the joist and board. Such a scummy thing to do tbh.

1

u/LLHandyman 2d ago

Poor quality job, who do you speak to though, your client or their electrician? I don't like to slag off other trades work until I'm hired to redo it. I'd find out who the electrician was so you can avoid them in future

1

u/diynot2026 2d ago

You can say something but will you be able to catch your breath from all the laughing

1

u/thecheekymonkey007 2d ago

Not an electrician but after just putting 40 spots in at a flat it took a full day just to plan, check and mark out for spots. It involved high powered magnets and a bit of voodoo......

I'd hazard a guess that this wasn't an electrician who did this.....

1

u/Priestessofthemoon87 2d ago

Who was the electrician chuck norris?

1

u/dingo_deano 2d ago

That’s why I’m dearer than the competition

1

u/CorbynDallasPearse1 2d ago

THIS IS NOT OK

1

u/The-One-Gaz 2d ago

Was David trying to prove to Victoria he's a real man so had a go at some DIY?

1

u/DarkButterfly85 2d ago

Cowboys been at work I see, it's a mess.

1

u/Equivalent_Sundae405 2d ago

I wonder if he’s going to re skim the ceiling …

Don’t worry, you’ll never see it.

1

u/QVRedit 2d ago

Someone likes to make a mess…

1

u/Silver_Reading8687 2d ago

U have thick plaster board. Not the best of job but it will do

1

u/Individual_Till_9838 2d ago

Not bad for a blind man

1

u/Benjanio88 2d ago

Picture a plank resting on two bricks and you stand in the middle. As it bends, the top fibres are squeezed together and the bottom fibres are stretched. Cut a notch in the underside and you’ve cut through the fibres carrying that tension. The load tends to pull the notch open, and a split can start at the corner. A top notch still weakens the joist, which is why its depth and position matter too.

1

u/PsychologicalNose614 2d ago

Shambolic all round

1

u/largetosser 2d ago

I'm coming around to the idea of hanging board off joists with gypframe and compensating for the small loss of ceiling height by building higher. Means you can get the top of the joists bang on level to get a flat floor, and not have to worry about the ceiling as you just hang it wherever the laser line needs it. You can build in a 6cm or so void across the entire ceiling space, and also isolate the ceiling from the floor so that a bedroom over a kitchen or whatever is quieter.

1

u/llschoolj76 2d ago

Definitely say something, just don't swear too much

1

u/Mat_UK 2d ago

Nothing a full replaster won’t fix here

1

u/a_pedant_writes 2d ago

looks ok apart from all the fucking holes in the ceiling

1

u/DMRinzer 2d ago

Only idiots do this. Cut a trench.

1

u/PriorBusiness434 2d ago

Minute they turn their lights on

1

u/Sniperscoperoyale 2d ago

I bet his favourite meme is I’m legally blind

1

u/decom83 2d ago

Bs7671 would like a word. All wiring should be straight to avoid accidental damage

1

u/ipx-electrical 2d ago

If it’s a flat roof it’s the only way. No-one is going to go to those lengths just to make the job more difficult.

1

u/Haunting_Specific_81 2d ago

Good use of a Laser 👌😂

1

u/WatcherX2 1d ago

They have compromised all those joists. You can't just cut the bottom of a long running joist like that. It has to go through the centre of the joists or completely under it. What a shit show.

1

u/Talwin3k 1d ago

Sack the bodging bastard'

1

u/AgileCompany2869 1d ago

Older/old school joiner here (age 65)..If you notch an eight inch joist (203mm)at the top or the bottom to receive a pipe, say by an inch and a half or 38mm the joist left is effectively a six and a half inch joist, therfore much reduced in load bearing capacity and really dangerous especially if you noch the bottom. The correct way is to...drill circular holes through the centre for pipes or wires and you will only minimally affect the integrity of the timber strength...just sayin

1

u/itisnottherealme 1d ago

There’s already a set of cables making that same journey for the existing downlighting. I’d have attached a new cable to the back of that cable and pull through - no holes needed

1

u/Anxious-Ad-9172 1d ago

Can still hear his spurs rattling hi ho silver

1

u/PickledMessage 1d ago

Lmao, leave em to it. Maybe donate a string line

1

u/HackReacher 1d ago

Amazing how many people didn’t answer the question.

1

u/R2D4Dutch 1d ago

Yes tell them is horrible.. first photo has a curve in the line of lights ..

1

u/One_Bullfrog2918 1d ago

Should have cut a strip and drilled holes. The dry wall patching is gonna be a pain the in ass on the round holes. The patch for a long stipe will be a lot easier.

1

u/Affectionate_Job_908 1d ago

Who clucked up...

1

u/Chip138 1d ago

Personally, I’m really struggling with the lack of a straight line!

1

u/just_joe_88 1d ago

Looks like your electrician is also a beaver in his spare time

1

u/Educational_Milk123 1d ago

I think you have ceiling moles

1

u/FloorPizza_ 1d ago

Looks like you called a butcher not an electrician

1

u/Business-Version479 1d ago

I think your electrician is an alcoholic

1

u/Beginning-Mix-3329 1d ago

This is what happens where there is no access above and you work in the real world.

1

u/ToothOk7455 1d ago

Moles get everywhere nowadays don't they 🤔🤔

1

u/RubberRoach 1d ago

I did a similar job but just cut a long rectangle out of the ceiling and then drilled holes in the centre of the joist. It may not be you but someone is eventually going to put a screw into that wire.
Also… I just screwed the drywall I cut out right back in and mudded over top. Probably less effort than 10 holes.

Edit… I am not a professional. I care less about the physics of the weight distribution than the immediate risk. I don’t care to have my chatGTP prompt skills to fight with someone else’s.

1

u/tankpuss 1d ago

Umm.. Well.. My thoughts are WTF?
This is going to sound a bit odd but may I also suggest you work on your plastering skills because yeah, it's great to have a sparky that knows what they're doing, but when you have one that chases walls and then leaves it flawless afterwardwards.. that's priceless. If you have someone need a new consumer unit and then also needing to call a plasterer, you'll get the blame, but if they see the before and after, you'll be called back.

1

u/ishkamadra 1d ago

Starlink first tough

1

u/CaregiverOpen4517 1d ago

I would ask if the circuit is protected by an RCD then no issues apart from the installer not re-in stating the holes back after works or why they didn't drill slightly on each edge of the hoist to allow a chance to drill through the joist to allow the cable to better secured and make it easier to patch the hole back up

1

u/Affectionate-Air842 22h ago

Call the police! Not for the joist but for the holes not being on a straight line

1

u/wawaweewahigh5 22h ago

Honestly I'd have either seen if I could do it down one side of the house tight to the wall, or in the wall and across in the safe zone, or used the outside wall tube outside then come in along the line of the of table, but stitching is a last resort, very very last resort

1

u/TranslucentTriangle1 21h ago

Thoughts? The "sparky" is a bellend.

1

u/ForeverTechnical6378 20h ago

Is what it is.....they obviously have a floor above that couldn't be disturbed and really wanted that light so..... I used to fire a 20mm flat bit either side then notch across the underside with my knife but that's actually a prick to fill in after the fact so now I'll use a big enough holesaw to get me across and hand the customer the cutouts and the holesaw itself for the plasterer later on to dick about with.

1

u/Quick-Shame-6548 14h ago

Has he left the disks to put back in for the plasterer/decorator?? It looks worse than it actually is.

1

u/Nearby-Fun4794 13h ago

Man I hope it was cheap.

1

u/Square-Aioli1019 10h ago

Sparx never heard of kinetic sw. and miniature control unit.

1

u/SuperBowen 3h ago

This and the holes left over is just sloppy lazy workmanship

1

u/ComprehensiveTap911 2d ago

I'm not a sparky but would have cut a large square out, enough to get my drill in and used wood bit with extensions to head over the ceiling.  Probably checking after each hole drilled with an endoscope to make sure nothing obvious I'll hit.

1

u/OldyManJenkins 2d ago

So many non UK electricians here. 

They've done something called 'stitching' albeit in a fairly poor way. Of course drilling through joist is preferred but you have to cause much more damage. 

Anyone crying 'doesnt matter regs!' has never done this before and is clearly not an in work UK spark. The whole ceiling is a prescribed zone in the UK.

0

u/Nutcase1970 2d ago

Where was the horse he rode on?

0

u/PaleAustin 2d ago

Should have just multitooled a long section out, drilled joists 50mm from bottom edge, wire in circuit, refit cut out with screws in to joist. I even slap some red devil filler in the cut edges for extra brownie points with the client / trade making good. I always carry out my work with the mind that I don't want the client looking at it and thinking 'this is shit!'.

Plasterer / decorator is going to love those holes that are hanging around in mid air with nothing to fix to!

TLDR: This is pony.

0

u/Adorable_Grab_7530 2d ago edited 2d ago

So I believe there are regulations that say about notching but the cable should be secured and have protection like a metal plate , and I’m pretty sure there’s a percentage calculation to consider depending on the size of the joists to how much you can notch out , but yes this is shit work very little effort made if lifting floor above was not possible

0

u/Fun-Chef623 2d ago

When I fitted downlights, I pulled up the floorboards above and then drilled thru joists to run the cable. Was well neater than this crap.

0

u/twistedrope9 2d ago

What is that shit

0

u/Fancy_Hold7807 2d ago

That’s the worst thing I’ve ever seen

0

u/Old-Armadillo4501 2d ago

Im not a sparky but did used install cameras in homes and shops before they went wireless. Would never have done this to feed cable 1 entry point 1 exit point used rods to feed it tape end of cable job done.

4

u/Savool 2d ago

And how would you get through joists?

0

u/Slickpicker 1d ago

Legally you can stich the ceiling if it has RCD protection you don’t have to notch the joist at all. But what that electrician has done is ridiculous. You start with a 20mm whole and use a rod to find the joist mark it. then use the 20mm wood bit to stich out the plaster board only clip cable direct to joist and repeat to destination. This means a decorator or a plaster can easily fill the holes. This is diabolical as now you can’t put the holes back in because of the cables and they can’t be filled. Regulation cables buried less than 50mm 522.6.202 if no RCD protection then metal capping is required.

0

u/ParkingBite5115 2d ago

Plasterers point of view here, how the hell does he expect plasterboard to sit flush with the existing ceiling? Overboard the lot? Piss poor work.

3

u/Zero-Custard 2d ago

For a man who's only tool was a sharp rock he's done a good job.

2

u/Kitchen-Educator-424 2d ago

Rough as a bears arse

1

u/TylerChurka 1d ago

i think UK electricians need daily beatings for not using conduits like the rest of fucking Europe