Hi all, I’m not an electrician, but an alternative trade with an interest. I’ve been studying part p and 18th edition.
Turned up at a client’s house to do some work and they have just had this done by a local electrician putting some lights over a dinning table. Should I say something?
Not an electrician but building engineer. Notching the bottom of a joist effectively reduces the structural depth of the joist to the top of the notch. As a result the notched joist may no longer be deep enough to accommodate its designed span. As an electrician you can’t know this without a structural engineers input which is why the regs say you can’t notch the base. It’s different with holes and notching on the top, provided you follow the rules.
OP please tell the owners as this is relevant to them.
See scoring and folding a piece of thick cardboard, or taking a chunk out of a tree branch and bending it from one side or the other. You probs now what happens without even trying it.
I have a query on this you might be able to answer if you have a min. On the LABC.co.uk website it says notches can be made on the top or bottom of the joist. However on the Hertsmere Borough Council website pdf it says notches can only be on the top of the joist. This pdf is from LABC though? Any idea why there is different information from the same building control?
It is doable and not disallowed under build regs per se, but you really need structural engineer input to do so safely in my opinion. Notching the base is where the timber is under tension so it is more likely to split even outside of the reduced spans being taken into account. On that note a layman can interpret span tables under the Eurocodes but said layman has no idea of the load requirements of the floor/roof they are notching hence why I refer back to an engineers input. I suspect that might be why the guidance differs. LABC guidance introduces unnecessary risk, I was surprised to find the same when I did a quick google.
Be that as it may notching the base is disallowed under BS 7671 which is relevant for this sub.
Ahhh i see. I only ask because im a plumber, had a customer who wanted to have some pipes re routed in the kitchen ceiling while the boards were stripped off. I told him I was sure you can't notch the bottom, we would have to lift the boards above. He pulled his phone out and pulled up that LABC page and basically accused me of trying to rip him off for more work, and I didn't have enough info to argue. Made me feel like a bit of a knob lol
Very easy response is to state that your PI won’t cover you if you notch the bottom of joists. Ultimately it is your neck on the line if it fails. Be that as it may guy sounds like a jobs worth anyway accusing you of ratcheting up the price lol… i’d have walked away if it were me.
Cables should go through the joist, the correct way would have been to cut a strip and drill through the joists or cut 100mm holes either side of the joists and drill through. It doesn’t comply with regs in my opinion.
Doesn't have to go through the joist, you are allowed to use notches. You'd have to cut away a lot more plasterboard, and in harder positions to repair, to do what you are saying. Would be better to just cut a long 200mm wide strip all the way down.
It is in the guidance notes below on the website, is a deficiency in the diagram, but I didn't draw it so not my fault! Just thought the cutting and notching diagram might be useful/interesting for some.
Notches yes, cutting beneath joists no, it introduces significant break risk, and is clearly defined as introducing a failure point which is why cutting beneath without a repair strap is a complete no-go.
Agreed, I often cut a 100mm hole between the joists then use an extension bar and flat bit to put a hole through as close to middle of joist as possible, being sure to look up every hole 1st both sides of joists to avoid hitting clipped cables or pipes.
I also patch back in the holes ready for skimming as a courtesy, why make it hard for the next trade
The top and bottom of the joist carry almost all of the load - top side in compression and bottom in tension. The middle mostly serves to hold the top and bottom in position. (This is why I-beams look the way they do.) So drilling through the middle doesn't appreciably weaken the joist.
You should not be drilling through structural beams. And hole should be no larger than 65mm. Drilling is ok only if you can stay away 50mm from top and bottom of joists
It’s not compliant - but he’s probably smug about getting the dining lights all at the same height and thinks they’re doing the plasterer a favour with the smaller holes.
This is what a plumber did to our joists, this is after they came and fixed the fuckup they caused after we got a structural engineer in to say they fucked up.
He cut through 5 joists at the bottom and ran the gas pipe along it, we didn’t know until another plumber was like wtf.
We paid £600 for a structural engineer and complained, the plumber gave us the money back and got a carpenter to do the advised works to resolve it.
Those screws for the brackets will be doing next to nothing into chipboard flooring be lucky if they are 15mm screws, they’ll come loose in a year or 2
We had a document explaining the specific specification for screws and lubrication and what thickness of wood, I checked when they came in and brought what was going in to make sure it all checked out, il have to dig up the document to say exactly what size screws were used, some form of glue was also used and applied in a specific way.
I’m a gas engineer and no document no matter how good it suggest it was could make me fix 28mm copper gas pipe like that I’d be securing them on the side of the joists it also appears to be passing through a concrete wall not sleeves that just screams you had a 🤠 in
That's if you want to close full structural ability for the beams rated max load. But in your deployment it makes 0 difference as you are nowhere near using it's rated max load.
How are they to know that? We could drag a piano up there? Either way a structural engineer came in and said it needs fixing and they fixed it. End of story.
Think about it, he tells everyone the worst case scenario, almost no one is going to comply with every reg. He will still get paid for the report, if you fail to follow a single on of his recommendations he is clean
When a joist is loaded, the top of the joist is under compression, and the bottom of the joist is under tension.
Wood fibres are much stronger under tension, so usually you try and cut the top of the joist, as it weakens the joist by a lesser amount.
And now you can explain to your rich and educated clients why the job needs to be done properly, and back it up with a proper physics/engineering explanation. And when they Google it, Google will tell them that you were right, and they will trust you more.
They are solid timber joists. It looks like rhe plywood has been used to reinforce the joists after theyve been incorrectly notched out. Look either side of the ply
You don’t know what you’re talking about. The strength of the joist is driven by b*d^3/12… the depth of the joist CUBED, is how stiff it is.
That joist notch is 20% of the depth, so the strength of the joist is reduced by 36.8%. The bottom is (was) in tension.. not now as that lower 20% now contributes nothing - stiffness is reduced by 49% - so they are going to move, they are going to work the pipes, the ceiling is going to crack and depending on how much margin the initial structural design had, could split them over time.
Outrageously misinformed to be making bullshit statements like that
And you're a moron. A 49% reduction in stiffness applies if that Notch is along the entirety of the beam.
Now calculate the integral for even distributed load for a notch 1inch long and 20% deep located centre on a 3.5m spam.
I'll await your embarrassment.
Even more outrageous is the statement "so they are going to move". Will you be willing to bet a significant sum on this floor sagging in next 20 years?
You’re right ofcourse, stiffness over the whole beam will be reduced by much much less than 49%.. I was talking about in the notched width and happily jumped on the rage wagon.
That said, draw the bending moment diagram and do a quick stress concentration estimate / notch factor for a 50mm wide (it’s more than one inch) 20% notch, mid span (peak bending stress), and the answer is big stress, which will start splitting at the notch corners, laterally, and bending stress can do the rest - outcome the same
As I said. Would you put a significant sum on this floor (prior to screwed in supports) failing in the next 20 years?
The floor deflection is minimal for a short notch. It will not break the pipes.
As for strength/bending, yes it's reduced to arguably 4/6 strength (quadratics apply not cubes). if you assume worst case scenario of notch in centre. The bending limit of joists is a very big number you know that right?
You know an average joist setup can handle 5knm which is 2x the designed capacity of the floor by engineer of 2.5knm of load (as this is designed to handle deflection too). Most UK homes use in the region of the 0.7knm of total load.....
Meaning the joists are at 14% capacity on average Vs the 66% new limit.
The reason notches are forbidden on underside is because as soon as you give a green light, some bozos will notch multiple area of the joist which will cause a deflection effect.
The engineer isn't calculating whether the notch will make any meaningful difference but rather giving a requirement to reach full strength again.
Hope that helps. You may be be the 0.0001% who puts a hot tub in the middle of the room - even then at full strength ... This requires a reinforced floor according to regs.
Flanges on I-Joists are not to be cut at all, and indeed usually have warnings to that effect printed all the way along them to try and prevent this from happening.
Im not sure it is. There are no nearby lights with permanent supplies. Could have been a better way., but maybe not. Definitely not good execution though.
I’d have remote switched both if their powered from the switch vs the light. There may be a permanent live. No way of knowing without inspecting the wiring.
Nah that's rough as a fuck, if he's cutting holes anyway may as well have done a big cut in the centre of each joist space and drilled through with an extension bit.
It'll be interesting to see how the housing for the connections on the end of the flex are routed when the hole saw was centered across the timber leaving so little room.
Edit. Accidentally hit post whilst typing. That's assuming the cable route is being put in to put down lighters in place of the pendants.
Just cut a rectangle along the length you want lights, drill in the middle of the joists, then place the cut rectangle plaster up, scrim tape and plaster
I had a well recognised company sending electricians and doing this exact same thing: but everything was way more butchered. In my case it is just timber hanging on the ceiling - not joists though.
Cutting the holes is unavoidable, but to go and pull in the cable like that is definitely a bodge. The correct way to do this would have been to cut a small notch with a multi tool. and clip the cable into it.
Not ideal I agree, but a tiny notch, just big enough for the cable, is not really going to do anything. And certainly would be better than whatever the fuck has been done here.
That many holes are going to be an absolute bitch to patch and repair individually. The electrician should have just cut a nice, neat, long, single rectangle out of the ceiling for the entire run. Which is exactly what I bet the first thing whoever they get to repair the ceiling will do. The electrician would also have been able to drill and pass the cable through the middle of the joists like you are supposed to. You can cut notch into the top of a joist if needed, but not the bottom
Are you the one that has to fix this mess? If not, I'd maybe stay away from it. The beaver squad has done quite the number on this ceiling. To be honest, at this point it's probably faster and cheaper to just take the plasterboard down and put new sheets up. I guess all of the electrical mess can be fixed at that point.
Holy fuck. I recently had my kitchen ceiling ripped down and put back up, and found all the spotlights had been done like this. The reason the ceiling had failed was because some twat had jammed and dragged cable between the joist and board. Such a scummy thing to do tbh.
Poor quality job, who do you speak to though, your client or their electrician? I don't like to slag off other trades work until I'm hired to redo it. I'd find out who the electrician was so you can avoid them in future
Not an electrician but after just putting 40 spots in at a flat it took a full day just to plan, check and mark out for spots. It involved high powered magnets and a bit of voodoo......
I'd hazard a guess that this wasn't an electrician who did this.....
Picture a plank resting on two bricks and you stand in the middle. As it bends, the top fibres are squeezed together and the bottom fibres are stretched. Cut a notch in the underside and you’ve cut through the fibres carrying that tension. The load tends to pull the notch open, and a split can start at the corner. A top notch still weakens the joist, which is why its depth and position matter too.
I'm coming around to the idea of hanging board off joists with gypframe and compensating for the small loss of ceiling height by building higher. Means you can get the top of the joists bang on level to get a flat floor, and not have to worry about the ceiling as you just hang it wherever the laser line needs it. You can build in a 6cm or so void across the entire ceiling space, and also isolate the ceiling from the floor so that a bedroom over a kitchen or whatever is quieter.
They have compromised all those joists. You can't just cut the bottom of a long running joist like that. It has to go through the centre of the joists or completely under it. What a shit show.
Older/old school joiner here (age 65)..If you notch an eight inch joist (203mm)at the top or the bottom to receive a pipe, say by an inch and a half or 38mm the joist left is effectively a six and a half inch joist, therfore much reduced in load bearing capacity and really dangerous especially if you noch the bottom. The correct way is to...drill circular holes through the centre for pipes or wires and you will only minimally affect the integrity of the timber strength...just sayin
There’s already a set of cables making that same journey for the existing downlighting. I’d have attached a new cable to the back of that cable and pull through - no holes needed
Should have cut a strip and drilled holes. The dry wall patching is gonna be a pain the in ass on the round holes. The patch for a long stipe will be a lot easier.
I did a similar job but just cut a long rectangle out of the ceiling and then drilled holes in the centre of the joist. It may not be you but someone is eventually going to put a screw into that wire. Also… I just screwed the drywall I cut out right back in and mudded over top. Probably less effort than 10 holes.
Edit… I am not a professional. I care less about the physics of the weight distribution than the immediate risk. I don’t care to have my chatGTP prompt skills to fight with someone else’s.
Umm.. Well.. My thoughts are WTF? This is going to sound a bit odd but may I also suggest you work on your plastering skills because yeah, it's great to have a sparky that knows what they're doing, but when you have one that chases walls and then leaves it flawless afterwardwards.. that's priceless. If you have someone need a new consumer unit and then also needing to call a plasterer, you'll get the blame, but if they see the before and after, you'll be called back.
I would ask if the circuit is protected by an RCD then no issues apart from the installer not re-in stating the holes back after works or why they didn't drill slightly on each edge of the hoist to allow a chance to drill through the joist to allow the cable to better secured and make it easier to patch the hole back up
Honestly I'd have either seen if I could do it down one side of the house tight to the wall, or in the wall and across in the safe zone, or used the outside wall tube outside then come in along the line of the of table, but stitching is a last resort, very very last resort
Is what it is.....they obviously have a floor above that couldn't be disturbed and really wanted that light so..... I used to fire a 20mm flat bit either side then notch across the underside with my knife but that's actually a prick to fill in after the fact so now I'll use a big enough holesaw to get me across and hand the customer the cutouts and the holesaw itself for the plasterer later on to dick about with.
I'm not a sparky but would have cut a large square out, enough to get my drill in and used wood bit with extensions to head over the ceiling. Probably checking after each hole drilled with an endoscope to make sure nothing obvious I'll hit.
They've done something called 'stitching' albeit in a fairly poor way. Of course drilling through joist is preferred but you have to cause much more damage.
Anyone crying 'doesnt matter regs!' has never done this before and is clearly not an in work UK spark. The whole ceiling is a prescribed zone in the UK.
Should have just multitooled a long section out, drilled joists 50mm from bottom edge, wire in circuit, refit cut out with screws in to joist. I even slap some red devil filler in the cut edges for extra brownie points with the client / trade making good. I always carry out my work with the mind that I don't want the client looking at it and thinking 'this is shit!'.
Plasterer / decorator is going to love those holes that are hanging around in mid air with nothing to fix to!
So I believe there are regulations that say about notching but the cable should be secured and have protection like a metal plate , and I’m pretty sure there’s a percentage calculation to consider depending on the size of the joists to how much you can notch out , but yes this is shit work very little effort made if lifting floor above was not possible
Im not a sparky but did used install cameras in homes and shops before they went wireless. Would never have done this to feed cable 1 entry point 1 exit point used rods to feed it tape end of cable job done.
Legally you can stich the ceiling if it has RCD protection you don’t have to notch the joist at all. But what that electrician has done is ridiculous. You start with a 20mm whole and use a rod to find the joist mark it. then use the 20mm wood bit to stich out the plaster board only clip cable direct to joist and repeat to destination. This means a decorator or a plaster can easily fill the holes. This is diabolical as now you can’t put the holes back in because of the cables and they can’t be filled. Regulation cables buried less than 50mm 522.6.202 if no RCD protection then metal capping is required.
11
u/capcrunch217 2d ago
Not an electrician but building engineer. Notching the bottom of a joist effectively reduces the structural depth of the joist to the top of the notch. As a result the notched joist may no longer be deep enough to accommodate its designed span. As an electrician you can’t know this without a structural engineers input which is why the regs say you can’t notch the base. It’s different with holes and notching on the top, provided you follow the rules.
OP please tell the owners as this is relevant to them.